I currently have 900w of solar going through a 40a CC into my 24v battery bank.
But during these winter months I get a maximum of 350w, 8a from the panels at the highest point of the day. This works out at maximum 2500w per day/1000w on overcast days.
I was thinking If i purchase two more of the same panels, could I use the same CC until spring at least?
Even doubling it up would only ever put 16a through the CC at any one time? Then come spring, I will spring for a new 150/85 Victron for the 4 panels.
Any ideas appreciated, also how I should configure the 4 panels? My CC has a max voltage of 100v.
Thanks!