timselectric
If I can do it, you can do it.
- Joined
- Feb 5, 2022
- Messages
- 19,550
Not normal, with a digital multimeter.there is no ac input this is off grid inverter for mining rig . And still when everything is disconnected from inverter , neutral to hot is 230v , hot to ground is 0v, neutral to ground is 0v. i called certified electrician to check he said that is normal if there is no ac input connected
It should be reading a voltage potential difference between conductive parts.
0v between neutral and ground would normally mean that they are bonded together. But 0v between line and ground would mean that ground is not bonded to neutral.
The two measurements are contradictory. (Impossible)
I would say that the meter is faulty. But the 230v between line and neutral is as expected.
So, while I don't know what is wrong. I can say that something is definitely not right.