I realize this is a lot to read, but the results are really worth it if you think about it - especially you
Dadoftheturkeykids given where you have your setup.
I was worried that my hasty calculations were wrong from yesterday so I redid them using 1 meter of cable -- and my old college chemistry/physics book
1 meter of 2/0 contains 0.611714kg of pure copper
Assuming 25c (room temp) to 105c where the insulation melts = 80c
Q (energy in joules) = mass * specific heat of copper * delta T
Q = 0.611714kg * 385 J/kg * 80c = 18813.1784J
Next ohms per meter is 0.0002426 for copper 2/0 welding wire.
power = current^2 * resistance Watts = i^2*r
Energy (joules) = power * time
P = 800a^2 * 0.0002426 ohms = 800a^2 * 0.0002426 ohms = 154.04W
T = 18813.1784J / 154.88W = 121.42 seconds
So in reality it would take 2 minutes at 800amps to get the wire hot enough to start melting insulation
Now I will assume 7000amps from each battery in the case of a dead short across all of them feeding back into one of the 2/0 wires
W = 28000a^2 * 0.0002026ohms = 158844W
t = 18813.1784J / 158844W = 0.1184 seconds
Now - MRBF fuse blow time from the mfg spec sheet - at 600% of rated current or 1200amps for this example
lists between 0.01 and 0.10 seconds
Now - since I have all the numbers I ask myself - how hot will the wire get in the 0.01s and 0.1s
P = 158844W (taken from above as the power of 28000amps)
t = 0.01 seconds from the chart
W = 158844 * 0.01 = 1588.44J
Now go back through the specific heat equations and you will get 6.75c temp rise -
so the wire starting at 25c (77F) will be 31.75c - Or 89.15F
Not even enough temp rise to get the wires warm before the fuses blow on all the batteries
Same equation but for 0.10 seconds = 25c + 49.74c = 74.74c == 166F
now the wire is to hot to touch but this is the long window and no fires started
Now the real MRBF have all blown
And in 1 second the wire would be 522.39c or 970F
Now we have a blazing fire if the wire is run any place that can catch anything nearby.
Melting point of copper is 1984F or 1085c --
It takes 2.13 second at 28000a to reach this point.
At 800 amps it takes 24 minutes.
If the fuse fails to blow we have a fire
super quick. With cheap no-name fuses this could happen. Now I expect any sort of fuse to blow sometime between to hot to handle and open flames and melted wires.
I personally didn't expect that result. Now from the shape of the curve the time gets shorter as the current goes up but in a LOG fashion.
What this tells me is all the wires between the batteries and the inverter should be inside metal conduit. For me at least it is eye opening.
This is why I check my work the next day - am but an egg (stranger in a strange land reference)
Now that I am all humbled by the numbers, I am really really interested in what you have to say, both of you.