Depends on model type.
Normal regular air conditioner with single speed compressor and thermostat with 1 or 2 degs C hysteresis will cycle less at night.
A 5 ton unit for 2500 sq ft house is on the overkill side unless your house is poorly insulated. 14 SEER is okay but still a little below typical more modern average of 15.
Typically thermostat works on temp with no regards for humidity.
Too high a btu unit for house area can cause temp to drop quickly and cycle off quickly with longer off period. This usually leaves house feeling like a damp cool cave. A/C only removes humidity when it is running when inside evaporator coils are cold and sweating water it condenses from inside air.
It takes much greater btu's to extract humidity from inside air then just cooling air around 50-60% relative humidity.
It is common for on to off duty cycle to get better at night as difference between outside and inside temp is less.
Some thermostats allow user to adjust the temp hysteresis to force a tighter temp control and decrease cycling period.
Power consumed when running is roughly 850-900 watts per ton (12,000 btu's), So 5 ton would be about 4400 watts (about 5 hp electric motor in compressor). Power factor is typically about 0.86 but changes based on compressor mechanical load. Around 15-16 amps at 240vac.
Max compessor load occurs for high outside temp, high inside temp, and high inside humidity. A typical condition if turning on A/C at 5 pm when you get home. Motor load can drop greater then 50% of maximum after inside temp and humidity is brought down. AC current does not drop so much because motor power factor decreases as mechanical low is reduced on compressor motor.
I have 4 ton central I run from two old series connected SW5548plus inverters. My central has Copeland scroll compressor which has a startup surge about as bad as you can get. I use a Micro-air EasyStart 348 cap boost/soft starter which gets the factory stock compressor startup surge from 200 amps @ 240vac down to 77 amps @ 240vac. Since poorer power factor results in greater inverter and cabling loss I use to 75 uF shunt cap for some PF correction improvement.
View attachment 58326
most importantly… how big is you pv array and how much battery?