I have a 48v 16s battery with this charge controller:
It says its rated for 60 amps, however it says the wattage max is only 2800w with a 160v input max.
My panels are 6.5 open circuit amps with 21.6v, so...
7 in series per pair = 151.2 volts
9 parallel pairs = 6.5 * 8 = 58.5 amps
Or 6,300 watts with 63 100watt panels.
Its still under ONE of the rated specs (amps) but not the wattage in the description. This descrepency is also in the instruction manual.
Should I ignore the wattage recommendation? This has "dumbed down for the normal people" written all over it.
I vaguely remember something about voltage drop over large distances, does that come into effect here? Like when the voltage drops does it automatically increase the amps flowing?
Edit: providing the link to the panels
It says its rated for 60 amps, however it says the wattage max is only 2800w with a 160v input max.
My panels are 6.5 open circuit amps with 21.6v, so...
7 in series per pair = 151.2 volts
9 parallel pairs = 6.5 * 8 = 58.5 amps
Or 6,300 watts with 63 100watt panels.
Its still under ONE of the rated specs (amps) but not the wattage in the description. This descrepency is also in the instruction manual.
Should I ignore the wattage recommendation? This has "dumbed down for the normal people" written all over it.
I vaguely remember something about voltage drop over large distances, does that come into effect here? Like when the voltage drops does it automatically increase the amps flowing?