I'm using a 50a T Tocas thermal circuit breaker on the output side of my 40 DC/DC charger.
I am getting a drop of nearly 1 volt at the breaker. So instead of charging at 14.4v, I'm getting 13.5v max. (I assume I'll be having the same issue with my Victron 100/30 as it has a 40a Tosca breaker on it.)
I assume this means I'll never reach a full charge on my battery (300Ah Enduro Power)?
Any suggestions?
EDIT: I was mistaken. There is no issue. Post 12 is what I have learned and I confirmed this with Renogy tech support. At this point, my charging system is working correctly.
I am getting a drop of nearly 1 volt at the breaker. So instead of charging at 14.4v, I'm getting 13.5v max. (I assume I'll be having the same issue with my Victron 100/30 as it has a 40a Tosca breaker on it.)
I assume this means I'll never reach a full charge on my battery (300Ah Enduro Power)?
Any suggestions?
EDIT: I was mistaken. There is no issue. Post 12 is what I have learned and I confirmed this with Renogy tech support. At this point, my charging system is working correctly.
I believe I was mistaken when I thought the breaker was causing a voltage drop. I think I was simply reading the battery voltage on that side of the breaker and mistook that as my charging voltage.