Class T fuse VS inrush current: Time Current Curve analysis

Johan

Off-grid energy systems enthusiast.
Joined
Oct 2, 2019
Messages
81
Location
Sacramento, CA, USA
Problem
It's very annoying when yet another expensive and hard to source class T fuse blows. So how can we visualize why they blow?

The graph below may explain why Class T fuses blow due to the inrush current from a (for example) LFP battery to an inverter. It may also explain why taking a fuse with the next higher current rating (e.g. 60A instead of 30A in the example below) does not always work. So the protective Class T fuse may need protection itself by a precharge circuit that limits the inrush current. Or mabe replace that fuse by a DC-rated breaker (with high enough AIR) that "ignores" the inrush current? Thoughts?

Notes
  • The Littelfuse Class T fuse graphs are way more tricky to extrapolate, that's why I am using Eaton/Bussmann Class T fuses here😬
  • Inductance is neglected, so the model may be a bit pessimistic.
  • Example inverter capacitance (C) values: Victron Multiplus-II 48/3000 120V: 4.42mF; Victron Quattro 48/5000 120V: 39mF.