I remeber dicussing this with you it would be interesting if you could one day test it. I would have to draw another picture to verify I understand your wiring suggestions.9 PV strings all in parallel.
With the busbars joined in the middle, there is a gap between breakers so they can't all be ganged as I suggested.
(With a hacksaw I could rearrange that pair of busbars to put breakers adjacent.)
What is Voc of the strings?
If high, that would contribute to sustaining an arc. It would also reduce the power lost with anti-backfeed diodes, if used.
I'll assume 7A or 8A Isc. Eight in parallel is 60A, more or less.
It would be interesting to see how a single backfed breaker behaves if one PV string gets shorted, takes the current from all others.
One of these days I'll buy a couple Midnight Solar polarized breakers and perform a destructive test. I've got plenty of PV strings I can set up for that.
Is this what your proposing so all breakers shutdown, just run a wire to combine them all?With more than two PV strings in parallel, OCP is supposed to protect a shorted string from carrying the current of two or more good strings backfeeding it.
With polarized breakers oriented to interrupt operating current in the normal direction, they are asked to trip under overload in the reverse direction. I believe they are likely to fail.
My proposal is to slip a wire through hole in handles of all the breakers, so if one trips it shuts off the others. The other breakers are carrying current in the proper direction so are able to interrupt current successfully.
With just three strings, 2x Isc is so close to allowed backfeed current I doubt it would actually cause harm to wires or interconnect.
If feeding through failed bypass diodes, those might have higher voltage drop than when in forward operation and at 2x current might overheat.
Although I think a shorted wire could handle 2x Isc, a breaker that couldn't interrupt the current would sit there carrying an arc, dissipating up to the watts of two strings in a small space. (A zero ohm short would carry full current with no power dissipation; all power would be dissipated across the PV string. An unknown impedance somewhere between zero and infinity would dissipate somewhere between zero and maximum array power.)
Besides ganging the breakers, other solutions I propose for polarized breakers are anti-backfeed diodes, or replacing them with either fuses or non-polarized breakers.
Is this what your proposing so all breakers shutdown, just run a wire to combine them all?
For my RV design, I wanted a way to shut the solar panels off from where I have my batteries and SCCs. For the midnite solar combiner that controlled the six panels on my roof, that is located in the same compartment. Because I have access to cut the flow of current in the compartment by flipping both breakers, I did not put an additional circuit breaker to shut the entire thing at once.think that might be the route I take as well. I will have three strings of three (3S3P) going into the box each going into a 15amp breaker and then the combined will go to the LV2424.
Done over again, I would not use a polarized breaker for my external portable panels after watching a you tube video where one caught fire after being set up the wrong way. I still would use dual pole, just not polarized.With polarized breakers oriented to interrupt operating current in the normal direction, they are asked to trip under overload in the reverse direction. I believe they are likely to fail.
Slipping a wire through the handles to trip more than one at a time just does not sound like a good idea. To me it seems like this wire would hold the C/B in the closed position instead of allowing it to trip to the open position. Are they designed for this?My proposal is to slip a wire through hole in handles of all the breakers, so if one trips it shuts off the others. The other breakers are carrying current in the proper direction so are able to interrupt current successfully.
Slipping a wire through the handles to trip more than one at a time just does not sound like a good idea. To me it seems like this wire would hold the C/B in the closed position instead of allowing it to trip to the open position. Are they designed for this?
I understand, but have never used the ganged circuit breaker.Schneider has 2, 3, 4 pole ganged DC breakers, providing higher voltage and/or interrupting both legs of the DC connection.
Midnight has 2 and 4 pole
Thanks for the reply.
Do you see any danger in bringing the three lines (6 wires) into the garage through Sch 80 conduit and then just using a 3 into 1 MC 4 on the neutral side, and a 15amp MC4 fuse on each string going into a 3 into 1 MC4 and then into the controller. It would use more wire, but then the fuses would be accessible on the ground instead of needing to get on the roof.
Hey Rich,Thanks for the reply.
Do you see any danger in bringing the three lines (6 wires) into the garage through Sch 80 conduit and then just using a 3 into 1 MC 4 on the neutral side, and a 15amp MC4 fuse on each string going into a 3 into 1 MC4 and then into the controller. It would use more wire, but then the fuses would be accessible on the ground instead of needing to get on the roof.
View attachment 31665
size AWG did you use on thesolar here, and what AWG did you combine it up wire
Can I ask: What size solar awg and what size combiner?
I have 12 of the 180w bougerv's coming and I wanted to use their 4 in 1 branch connectors to step up to 24v to match my growatt 3000w.
Would you like to tell me if I'm off?
Thx anyone & everyone for their 2c!
24P SOLAR CHARGER:
Maximum PV Array Power 2000W;
MPPT Range & Operating Voltage 30VDC ~ 115VDC;
Max PV Array Open Voltage 145VDC;
Maximum Solar Charge Current 80A;
BougeRv 180w (x12) 12v
Max. power voltage(Vmp): 18V
Max. power current(Imp): 10A
Open circuit voltage(Voc): 21.6V
Short circuit current(Isc): 11A
Series fuse rating: 15A
Max. system voltage: 1000V DC
J-Box IP Rating: IP65
You will be slightly over-paneled, but you would have to have a laboratory/perfect type day to get anywhere close to max.
Thanks so much, learning as I go!I ended up using 12 awg wire from the roof to the combiner box (~25 feet each string). Each string is ~100v and ~8.5a and connected to a 15amp breaker. The combined output is ~100v at ~25a and that goes from the combiner to the MPP Solar LV2424 via 6awg wire (about 2 feet). No issues over the last six months.
I think given your specs above I would also run 4S3P as you mentioned. If you series 4 panels together you would need a total of six wires from the panels to the combiner box which is what I have as well. That would give you strings at ~72v and 10a, and combined ~72v at ~30a. You will be slightly over-paneled, but you would have to have a laboratory/perfect type day to get anywhere close to max.
Thanks for the idea...I like the mixed angle idea."An ugly wood 'solar pantry' and pallet stands for panels "
By the profile and photo, panels are on portable ground mounts (if you ever get high winds, drive some stakes into the ground to anchor them.)
If you orient some series strings towards morning sun and some towards afternoon, that extends hours of production and reduces peak. At a 90 degree angle (6 hours difference), area presented to sun is just 0.7 times as much as a single orientation, so you could put in 40% more panels without having production clipped due to overpaneling.
Only thing I don't like is "Max current of single PV input array is 10A" You will be right at the limit, possible over.I'm looking at this combiner box from Eco-Worthy (not an affiliate link!): whould you trust it?
My Panels (x 4S3P):
- Input Circuits/Circuit Breakers: 6
- Circuit Breaker Rating: 10A
- Max Total DC Output Current: 60A
- Max Input Voltage Rating: 250V
- Max Output Voltage Rating: 250V
SO...does this eco-worthy combiner pass the sniff test?
- Max. power current(Imp): 10A
- Open circuit voltage(Voc): 21.6V
- Short circuit current(Isc): 11A
- Series fuse rating: 15A
- Max. system voltage: 1000V DC
Amazon.com : ECO-WORTHY 6 String PV Combiner Box & 63A Circuit Breakers for Solar Panel : Garden & Outdoor
Amazon.com : ECO-WORTHY 6 String PV Combiner Box & 63A Circuit Breakers for Solar Panel : Garden & Outdoorwww.amazon.com
Doesn't matter: not certified in Canada so it's off the list. Thanks Rich!Only thing I don't like is "Max current of single PV input array is 10A" You will be right at the limit, possible over.
I almost ordered that and went with a mod it’s MNPV-6I'm looking at this combiner box from Eco-Worthy (not an affiliate link!): whould you trust it?