Connecting busbars with high current fuses?

I mean busbars!
The claim of the 4 stud buss bar is 250 amps and each stud is capable of 62.5 amps so as you can see the math for the size does not add up. So the answer is no.
And to add the bars are plated brass.
 
Last edited:
There could be. Fuses are relatively high resistance and cause a voltage drop under load. In most cases I think you'd prefer to have two bridged bus bars as close as possible to one voltage.

But if you understand the implications of the voltage drop, and it does not cause a problem for your circuit, then it could be fine.
 
And not meaning to discourage you but your fake gold plated fuses are high resistance. I would recommend copper fuses if you want the good stuff.
 