DIYrich
Solar Wizard
When all inverters are charging, don't exceed max charging rate of the battery. Don't exceed the max draw rate of the battery when all inverters are max drawing power.
Or a common battery. Which is what they want to do.I missed that part. Yes, then a separate battery for each system.
Trying to wrap my head around how this would be (unless both inverters are off grid, or you get L1 tangled up with L2).Connecting them to the same battery shouldn't matter I agree, but better not connect them to the same ac panel..
Magic smoke !
If units are connected together on the AC output. They must also be connected together with communications cables. (So that they act as one)Trying to wrap my head around how this would be (unless both inverters are off grid, or you get L1 tangled up with L2).
Load side is AC output side.What about load side AC coupling?
I meant high voltage MPPT and intermediate bus systems not battery. Battery still 48VHigh voltage battery systems are definitely a different animal.
Nothing said here applies to them.
Are you talking about over 600v?I meant high voltage MPPT and intermediate bus systems not battery. Battery still 48V
Are you talking about over 600v?
If so, then yes. That's also on a different level.
That wasn't because two units were connected to the same battery, without communication.I would like to chime in here. I have concerns about two inverters using the same battery without comms.
Complete off grid.
I had a growatt 5000es hooked up to my generator charging my 48v battery( only using as charger) no AC output hooked up at all. Just Genny. Breaker. Battery bank. On the same battery I had my solark 15K hooked up powering my house loads. Reason I did this is to avoid flickering lights in the house when Genny on. Worked great UNTIL one morning I was charging with this setup and solar started producing. As soon as solar power coming into solark (again NO solar hooked up to growatt). As soon as solar soming into solark overtook the loads in house and started also charging the batteries. pOOF. Fried the growatt. Tripped my breaker. Tripped all my BMS for over current and shut everything down.
I have a thread about it you can search.
Since the solark is still powering my house as I sit typing this. I'd say the growatt was the weak link. I have the new SRNE 10K hooked up in the same fashion now and it is a backup inverter for the whole house should we need it. But I'll only use it for charging at night in this fashion when both inverters are drawing just to be on the safe side. Those mistakes cost thousands. I'd rather buy more batteries.That wasn't because two units were connected to the same battery, without communication.
It was either an internal failure in the Growatt. Or a voltage surge from the Sol-Ark, that damaged the Growatt.
I would think a chargeverter is likely designed to coexist with other chargers, like standalone MPPTs are.Since the solark is still powering my house as I sit typing this. I'd say the growatt was the weak link. I have the new SRNE 10K hooked up in the same fashion now and it is a backup inverter for the whole house should we need it. But I'll only use it for charging at night in this fashion when both inverters are drawing just to be on the safe side. Those mistakes cost thousands. I'd rather buy more batteries.
I didn't think I was doing anything wrong with my setup. You can check my YouTube video. However I am cautious now and only charge at night to avoid any possible issueIsn't there a presumption that the charger on the AIO is tolerant of overvoltage?
An AIO that is designed to never stack, or only natively stack, may not need overvoltage protection to satisfy the manufacturer documented use cases.
I would like to see if maybe the chargeverter has a large diode in it that doesn't allow backward flow of current into it. Only out of it. That's the solution in my mind.I would think a chargeverter is likely designed to coexist with other chargers, like standalone MPPTs are.
Could be like how FET based BMS police the power flow direction. It’s often with ideal diodes when the real power level kicks in.I would like to see if maybe the chargeverter has a large diode in it that doesn't allow backward flow of current into it. Only out of it. That's the solution in my mind.
Since it was the Growatt that failed. It was definitely the weakest link.Since the solark is still powering my house as I sit typing this. I'd say the growatt was the weak link. I have the new SRNE 10K hooked up in the same fashion now and it is a backup inverter for the whole house should we need it. But I'll only use it for charging at night in this fashion when both inverters are drawing just to be on the safe side. Those mistakes cost thousands. I'd rather buy more batteries.