Problem:
I’ve got a Soladeck through-roof junction box with cable glands that accept wire OD of 7.4mm (0.2913”) maximum.
I’m trying to feed a new 3P1S parallel string into that junction box which means I’ll need a short length of 10AWG PV wire running out of the junction box into a Staubli MC4 connector rated for 60A up to 50C.
10AWG PV wire is rated for 55A up to 90C if freestanding in air (not in conduit, single + and - short 10AWG wires will be run from junction to 6AWG within junction box out through cable glands into air where they will connect to Staubli Y connectors rated for 50A @ 85C).
If I use the Iscmax x 125% x 125% x 3 panels in parallel calculation, wire needs to be sized to handle at least 41.17A and I believe I should be OK (as long as I am using the correct Saubli MC4 connector), but I’d appreciate a reality check on anything I may be overlooking tag would translate to this circuit being unsafe.
Here is the datasheet for the Staubli MC4 connectors: https://www.staubli.com/content/dam/spot/PV_SOL-LVDC-en.pdf
Section 4.1 indicates that the PV-KBT4/6X MC4 connector has a cable gland supporting cable OD range of 5.7mm to 7.4mm which is the size I need to fit my 10AWG PV wire with an OD of 0.28” = 7.112mm.
The Current Derating Diagram on page 9 shows that the MC4 connectors connected to 10AWG / 6mm2 PV wire (purple) are rated for ~50A @ ~50C and ~30A @ ~90C while the table at the top of page 10 specifies a rating with 6mm2 cable of 60A @ 50C and 31A @ 90C.
Ambient temps on my roof never exceed 120F / 48.9C, so a temperature derating to 50C should suffice.
Does anyone see a reason that putting a 3P1S string with a worst-case ISC current of 26.3A (41.166A @ 125% x 125%) through one of those Staubli MC4 connectors connected to 1-2 feet of 10AWG PV wire freestanding in air (and shaded by a PV panel) could be a safety hazard I might come to regret?
I’ve got a Soladeck through-roof junction box with cable glands that accept wire OD of 7.4mm (0.2913”) maximum.
I’m trying to feed a new 3P1S parallel string into that junction box which means I’ll need a short length of 10AWG PV wire running out of the junction box into a Staubli MC4 connector rated for 60A up to 50C.
10AWG PV wire is rated for 55A up to 90C if freestanding in air (not in conduit, single + and - short 10AWG wires will be run from junction to 6AWG within junction box out through cable glands into air where they will connect to Staubli Y connectors rated for 50A @ 85C).
If I use the Iscmax x 125% x 125% x 3 panels in parallel calculation, wire needs to be sized to handle at least 41.17A and I believe I should be OK (as long as I am using the correct Saubli MC4 connector), but I’d appreciate a reality check on anything I may be overlooking tag would translate to this circuit being unsafe.
Here is the datasheet for the Staubli MC4 connectors: https://www.staubli.com/content/dam/spot/PV_SOL-LVDC-en.pdf
Section 4.1 indicates that the PV-KBT4/6X MC4 connector has a cable gland supporting cable OD range of 5.7mm to 7.4mm which is the size I need to fit my 10AWG PV wire with an OD of 0.28” = 7.112mm.
The Current Derating Diagram on page 9 shows that the MC4 connectors connected to 10AWG / 6mm2 PV wire (purple) are rated for ~50A @ ~50C and ~30A @ ~90C while the table at the top of page 10 specifies a rating with 6mm2 cable of 60A @ 50C and 31A @ 90C.
Ambient temps on my roof never exceed 120F / 48.9C, so a temperature derating to 50C should suffice.
Does anyone see a reason that putting a 3P1S string with a worst-case ISC current of 26.3A (41.166A @ 125% x 125%) through one of those Staubli MC4 connectors connected to 1-2 feet of 10AWG PV wire freestanding in air (and shaded by a PV panel) could be a safety hazard I might come to regret?