Could Liquidtight Flexible Metal Conduit be used throughout the installation? There seems to be some discrepancy as to whether MC Cable can be run exposed to the weather.PV cables when greater than 32 volt must be in metal conduit when on the roof and when entering and inside a building
PVC conduit can be used outside to bring the PV cables to the house JBox converting to metal
YesCould Liquidtight Flexible Metal Conduit be used throughout the installation?
How is the transition made? What connectors are you using in the box?I’ve found thhn to be much easier to pull in a conduit and less expensive than PV wire. PV wire is better for UV exposure than thhn. So for me logic dictates the use of a transition box to take advantage of each wire’s attributes.
You can run PVC conduit outside of a structure.Could Liquidtight Flexible Metal Conduit be used throughout the installation? There seems to be some discrepancy as to whether MC Cable can be run exposed to the weather.
Din rail terminal blockHow is the transition made? What connectors are you using in the box?
What you can do it run PV wire into a box, either NEMA 4 and install a junction block or you can use something like a PV disconnect such as the IMO. Mount the IMO outside of the structure, then run metal conduit into the structure. This allows you to not only transition the wire but also the conduit.How is the transition made? What connectors are you using in the box?
I was under the impression I could not run it if the voltage was higher than 32 volts, had to be MC.You can run PVC conduit outside of a structure.
Outside the structure can be PVC.I was under the impression I could not run it if the voltage was higher than 32 volts, had to be MC.
It doesn't have to be in metal conduit until it enters the house.I was under the impression I could not run it if the voltage was higher than 32 volts, had to be MC.
Thank you for your input. I was planning on running the PV wire into a NEMA 4 junction box to make the transition to THHN. The IMO disconnects are located as soon as the wires come into the structure. The run from the roof to the point where they enter the structure is about 15ft. Everything being equal I would just assume to run the Liquidtight Flexible Metal Conduit from start to finish. An spd did not cross my mind, I am in California. Should this be of concern?What you can do it run PV wire into a box, either NEMA 4 and install a junction block or you can use something like a PV disconnect such as the IMO. Mount the IMO outside of the structure, then run metal conduit into the structure. This allows you to not only transition the wire but also the conduit.
The other choice is a box like the Vevor I used. You mount a DIN rail inside with a breaker and SPD's. You make the transitions there, mount it outside the structure and transition to metal conduit into the structure.
Okay. It's becoming clear. It's better to keep asking and avoid a costly mistake. Thank youIt doesn't have to be in metal conduit until it enters the house.
Ahh ok. Ive always used those midnite combiners w/breakers to make the transition. I just didnt have a better idea without long runs of PV wire.Din rail terminal block
Im glad you didnt say wire nuts
Why?Im glad you didnt say wire nuts
MC Run on the roof though???Yes, MC will meet the NEC code for PV. I run MC to my charge controllers, it is shown in a video about the EG4 MPPT's I did last year.
Just remember to use the plastic bushing on the ends to prevent wire chafing.
It will have a lower temperature rating though. 60C when wet. This will be quite relevant for temp and CCC derating
I feel like i opened a can of worms here, but really??Why?
Perfectly fine.
That's what I have used.
No idea why that would be.I feel like i opened a can of worms here, but really??
Im just curious because I was taught to steer clear of wire nuts for DC
(Metallic liqudtite)