DC Ground Fault Protector

Robkh

New Member
Joined
Jun 8, 2022
Messages
42
Location
Phoenix, AZ
Building 4000W solar array to power two EG4 6000XP inverters in parallel with two EG4 PowerPro batteries in parallel.

I read the NEC requires a DC ground fault protector to disconnect PV+ line to prevent fires.
So I called Signature Solar tech help and they don’t sell the device and do not believe it is necessary.
Any opinions?
 
EDIT: see my next post first


I bought this: https://www.midnitesolar.com/productPhoto.php?product_ID=252&productCat_ID=16&sortOrder=4&act=p

Is it necessary? The only thing it does is disconnect when it senses current on the ground conductor from the PV+.
It does not tell you where the fault is. It will not detect double faults.

I put it in to satisfy code, otherwise, meh.
It is a high quality 50A breaker at least. But code says you can’t use it as a disconnect!
So I’ve also got an inexpensive two-pole 50A Langir breaker for that.
Nice avatar.
 
Last edited:
The 6000xp has a “pole sensitive leakage current monitoring unit”
Ask signature solar what that means, sounds like ground fault detection to me.

Actually, Page 6 of the manual explictly says it has arc fault and ground fault pv protection.
You are compliant.
IMG_6615.jpeg
 
Last edited: