A few days ago, I got a jolt when I tried attaching a Temperature Probe onto the heatsink. I realized the case GND connection corroded resulting in ~40VAC case/heatsink to floor/wall. So I want to redo case grounding.
Q1: For this Deye's case grounding purpose, can I use a solid #14 wire? Or must it be same size as L1, L2 wire?
On this photo, I measured that these PE terminals inside the inverter have zero resistance to case and heatsink.
Because of previous corrosion experience, I thought of using these for grounding.
Q2: Is this allowed/safe? or is Grounding can only be done on the case?
Q1: For this Deye's case grounding purpose, can I use a solid #14 wire? Or must it be same size as L1, L2 wire?
On this photo, I measured that these PE terminals inside the inverter have zero resistance to case and heatsink.
Because of previous corrosion experience, I thought of using these for grounding.
Q2: Is this allowed/safe? or is Grounding can only be done on the case?