My first post was on Dec 20/2020 and I see now I had no idea, Thanks to Mr. Sandels and six weeks of reading posts, energy audit, purchase of a current meter I feel I have a small grip on things
Please see system size calculations below
My system will consist of:
- 60 amp Critical electrical Panel with 18 single 15 amp fuses (Completed)
- 16s2p Lishen 272 amp cell configuration, for (272a X 3.2v X 16pc) =13,926ah X 2 banks =27,858ah Storage.
- 2pc MMP Solar 6548, 6500watt all in one inverter. 6500w X 2 =13,000w with 6000w X 2 = 12,000w surge.
-Positive 2/0 wire from cells, - T type fuse 250 amp, - emergency 300 amp shut off switch, to Positive copper Bus Bar, same configuration for each for the 2 Parallel 16s cell banks.
-Negative 2/0 wire from cells, - BMS 200amp, - Shunt 200amp, Negative Bus Bar, same configuration for each for the 2 Parallel 16s cell banks.
-Positive and Negative 2/0 wire from Bus Bar to each MMP Solar 6548, 6500watt
Solar, 5.92 kw total, 16 panels Mono Cell, 370w Open circuit VOC 47.8v, Power VMP 38.9v, Short circuit 9.88A, Power current 9.52A, much more work to be done on calculations, string orientation, roof drawings, engineering to come.
If I could get some INPUT and CRITICISM on my Cell packs, fuse size and type, BMS size, wire size I would be more than HAPPY
Please see system size calculations below
My system will consist of:
- 60 amp Critical electrical Panel with 18 single 15 amp fuses (Completed)
- 16s2p Lishen 272 amp cell configuration, for (272a X 3.2v X 16pc) =13,926ah X 2 banks =27,858ah Storage.
- 2pc MMP Solar 6548, 6500watt all in one inverter. 6500w X 2 =13,000w with 6000w X 2 = 12,000w surge.
-Positive 2/0 wire from cells, - T type fuse 250 amp, - emergency 300 amp shut off switch, to Positive copper Bus Bar, same configuration for each for the 2 Parallel 16s cell banks.
-Negative 2/0 wire from cells, - BMS 200amp, - Shunt 200amp, Negative Bus Bar, same configuration for each for the 2 Parallel 16s cell banks.
-Positive and Negative 2/0 wire from Bus Bar to each MMP Solar 6548, 6500watt
Solar, 5.92 kw total, 16 panels Mono Cell, 370w Open circuit VOC 47.8v, Power VMP 38.9v, Short circuit 9.88A, Power current 9.52A, much more work to be done on calculations, string orientation, roof drawings, engineering to come.
If I could get some INPUT and CRITICISM on my Cell packs, fuse size and type, BMS size, wire size I would be more than HAPPY