Now that you mention it, what I need is a IMPORT power limit.
Before you say it, there is a parameter where you set how much current can come from the grid connection GdCurNom (232.03) (for example mine is set to 55amps)... If I set it to 1 amp then I can only push OR pull 1amp. So I have to set this to 55amps. So that won't limit import power without also limiting export power.
When I tried that parameter, it did not disconnect to prevent export of excess power above the limit. Maybe your firmware handles it differently. Mine was an older 5048US, firmware not updated.
Just use that parameter. If battery gets low, set it back up to 55A until SoC is back up where you want. If your SI does disconnect due to excess export (does it then cycle on and off grid repeatedly?) set it to 55A until you are once again importing, then set back to 1A.