I wondered if that was a knock off SCC… I did take a reading at the battery after panels, controller and battery connected, and I was reading 13 and change. what you said about too many volts makes sense.
13V at the battery is OK, indicates full battery if not charging and less than full if current is coming in from the PV panels and charger.
13V would not damage the inverter.
I ran two panels in series. And then ran the two sets parallel. and which gave me about 74 V total when I took a multimeter reading. I guess I will go to parallel for all four panels.
74V is higher than you should ever see with two panels in series "2s". Same with two of those strings in parallel "2s2p".
24V per panel, should only reach 48V not 74V.
Seems to me you might have actually had all four in series.
Do you have a recommendation for an SCC and an inverter for the panels I have?
Pool pump is 3.2 A ,which gives us 16 A starting power x 120=1920 watt . So I need a 2000 watt inverter? 24V 200ah battery?
3.2A x 120V = 384W
Your panels only total 200W, and that would be under ideal conditions. Would need 2 hours full sun to run pump for one hour. With the sun off angle most of the time, you may get 6 hours effective sun in the summer, 2 hours in the winter.
Cycling battery, 3 hours run time in the summer would be the most you could hope for. Lead-acid battery will wear out with cycling, 1 year for cheap AGM, 2 years for quality AGM, a month for automotive starting battery. And that's assuming you don't over-discharge. Inverter low voltage cut-out probably too low to protect battery.
Would be better to put up about 1000W of panels, half oriented for morning sun and half for evening.
If that SCC can actually meet the specs on label, it might work. PWM should work OK with PV panel operating voltages like the ones you have. Are the SCC terminals big enough for a wire that can carry 100A??
The 1000W DeWalt inverter has 2000W peak, this should be enough to start 350W inductive load.
The DeWalt DXAEPI1000 Professional 1,000 Watt power inverter delivers enough heavy duty power to run tools and portable electronics on the job site or on the go. It's one of the most versatile inverters
www.homedepot.com
"
"
But we don't know if that is for 100 milliseconds, or for 3 seconds.
Need whole seconds for it to be able to start.
Other idea, I have not tested with pump yet though, is soft start module. It is a triac motor control module with automatic speedup over 1-2sec.
People report great success with MicroAir Easy Start. But cost is about $350.
Induction motors are difficult to start. Inverter drive and brushless DC are easier.
Can you find a DC pump to install instead, which could run off a 12V or 24V battery?