Zwy Solar Wizard Joined Jan 3, 2021 Messages 5,847 Location Timbuktu, IA Oct 21, 2021 #1 Interesting video, surprising results
D douglasheld New Member Joined Oct 9, 2023 Messages 43 Location London, United Kingdom Feb 3, 2024 #2 TLDR, at 4:10 the Victon Energy 100A fuse doesn't blow until 240A! There must have been a whole batch of fuses stamped with the wrong value.
TLDR, at 4:10 the Victon Energy 100A fuse doesn't blow until 240A! There must have been a whole batch of fuses stamped with the wrong value.
M MattiFin Solar Enthusiast Joined Dec 31, 2020 Messages 692 Feb 3, 2024 #3 douglasheld said: TLDR, at 4:10 the Victon Energy 100A fuse doesn't blow until 240A! There must have been a whole batch of fuses stamped with the wrong value. Click to expand... Nothing unusual there, typical 100A ANL is supposed to blow between 0.8 to 10 seconds with 250% load.
douglasheld said: TLDR, at 4:10 the Victon Energy 100A fuse doesn't blow until 240A! There must have been a whole batch of fuses stamped with the wrong value. Click to expand... Nothing unusual there, typical 100A ANL is supposed to blow between 0.8 to 10 seconds with 250% load.
C ChrisG Solar Addict Joined Sep 23, 2019 Messages 1,557 Feb 3, 2024 #4 I’ve used the blue sea resettable breaker/fuse for a long time and they have been fine. Running 120a fuse per 100ah 48v pack. Considering changing to MBRF. Last edited: Feb 3, 2024
I’ve used the blue sea resettable breaker/fuse for a long time and they have been fine. Running 120a fuse per 100ah 48v pack. Considering changing to MBRF.