I've had a Growatt SPA3000 installed with the Topband RS-R 5.12kWh rack batt connected over CAN. I've not yet had luck from either manufacturer for support. The Topband BMS is advertised as supporting Growatt inverters.
The SPA3000 does not show any fault code, but the Cb/Vb is listed as 0v, the inverter remains in standby, and no battery charge status shows on the display. The inverter will not charge or discharge the batt.
The DIP switches are set per the manual, and if I change them I do get a 'BMS Comms' fault so I assume that they are talking when on the right setting as this fault clears.
Is there any setup I am missing? Much of the material I can find seems to be for one of the other Growatt inverters (eg. SPF) with different settings that let you pick CAN protocol, eg. L51/L52. I cannot find this setting on the SPA, only changing the 'mode type' with a battery option for Lithium or Lead-acid. The batt type is set to Lithium.
Thanks!
The SPA3000 does not show any fault code, but the Cb/Vb is listed as 0v, the inverter remains in standby, and no battery charge status shows on the display. The inverter will not charge or discharge the batt.
The DIP switches are set per the manual, and if I change them I do get a 'BMS Comms' fault so I assume that they are talking when on the right setting as this fault clears.
Is there any setup I am missing? Much of the material I can find seems to be for one of the other Growatt inverters (eg. SPF) with different settings that let you pick CAN protocol, eg. L51/L52. I cannot find this setting on the SPA, only changing the 'mode type' with a battery option for Lithium or Lead-acid. The batt type is set to Lithium.