Growatt SPF5000ES is not charging the battery completely

Paulfrench35

New Member
Joined
Feb 20, 2023
Messages
75
Location
France
Hello, my SPF5000ES does not charge the battery completely, it stops for no reason.

It indicates a full battery while the voltage is 53.6v. I set #19 and #20 to 55.1v so why isn't it charging the battery?

The BMS indicates approximately 3.351v per cell while the Remain Battery is at 99%...impossible!!!!

My settings are not correct?

IMG_5628.PNGIMG_5629.jpegIMG_5630.jpeg
 
There is no absorption time, programs #19 and #20 have the same values as indicated in the manual. It's not good?

I don't have link CAN or RS485 between inverter and bms.

Capture d’écran 2023-10-13 à 14.29.22.png
 
Here are the observations based on what is posted.
1) The BMS indicates -0.4A and the arrow on the inverter display is pointing from the battery towards the inverter. This is exactly the expected voltage of an LFP battery that has been fully charged and is now sitting idle with no load or a very small discharge current. The battery must have completed a charge cycle at some point in the recent past and stopped charging. Unless the inverter enters into float mode the voltage will not be held high above the normal resting voltage.
2) The inverter shows a 4.6% load which is only 230W. So the battery is providing 53.6V x 0.4A = 21.4W and the remainder from Solar.

This behavior does not seem unusal. What specifically is the issue you are trying to solve?

EDIT: Per the inverter message regarding setting. User-Definded 2, it states that the inverter will stop charging when the battery reaches the setting. Seems like this is exactly what happened.
 
19 and 20 should not be the same.
Set 19 to 55.5 , or higher.
 
Last edited:
I charge at 55.6 volts. Hold that for 2 hours, then float at 54 volts.
The yellow dip is the changeover from absorption to float. Takes about 6 minutes.
 

Attachments

  • Screenshot_20231013-141043.png
    Screenshot_20231013-141043.png
    115.9 KB · Views: 5
My tp6048 (which may not apply to this since its not the same) has this for option 21.

Battery stop charging voltage
when grid is available

I was set to 54v but it has an option of FUL which seems to mean fill it up :)

When set to full it charges till the battery is completely "full" then goes to float.

Even though it says when grid is available it will charge to full on solar when no grid available. Go figure.
 
I followed your advice and it works much better.

Another question, why does the inverter refuse to let me go below 50v for program #12 ?

I would like to go to 49.8v.

A special rule to follow that is linked to another program #?

F40B363B-52C8-4492-A4E6-1221AF820B7D.jpgIMG_5640.jpeg
 
It can be set to anywhere between 44v to 51.2v .
But must be higher than setting #21.
 
How many volts minimum between both ?
I don't think that there is a minimum.
So, 0.1v should be fine.
Although, I wouldn't want it that close. It would be too easy to trigger an unwanted shut down.
I would recommend at least 2v difference.
 
Hi. I and I'm having a similar issue here with my batteries not getting charged up. They seem to max out at about 70-74%. I am new to LifePo4 batteries so I may have some of my settings off.

Inverter: Growatt SPF 6000T DVM
BMS: JK-PB2A16S-20A.
Batteries: EVE 304Ah x 16 for a 48v bank.

Inverter settings:
Prog 5: USE with no communication between inverter and bms
Prog 19: 55.6v
Prog 20: 54.4v

Below are pics of the bms stats and settings.

I noticed that on the inverter the battery voltage typically shows about 0.8v higher than the bms. Can I adjust the inverter to account for this variance?

I have also tried the these same settings in Progs 19 & 20 with the inverter set to US2 in Prog 5.



JK Model & Version.jpegJK stats.jpegJK settings 1.jpegJK settings 2.jpegJK settings 3.jpegJK settings 4.jpegJK settings 5.jpeg
 
Hi. I and I'm having a similar issue here with my batteries not getting charged up. They seem to max out at about 70-74%. I am new to LifePo4 batteries so I may have some of my settings off.

Inverter: Growatt SPF 6000T DVM
BMS: JK-PB2A16S-20A.
Batteries: EVE 304Ah x 16 for a 48v bank.

Inverter settings:
Prog 5: USE with no communication between inverter and bms
Prog 19: 55.6v
Prog 20: 54.4v

Below are pics of the bms stats and settings.

I noticed that on the inverter the battery voltage typically shows about 0.8v higher than the bms. Can I adjust the inverter to account for this variance?

I have also tried the these same settings in Progs 19 & 20 with the inverter set to US2 in Prog 5.



View attachment 245035View attachment 245036View attachment 245037View attachment 245038View attachment 245039View attachment 245040View attachment 245041
Update and question.
Here are the current stats. The BMS shows all of the batteries around 3.275v (52.4v total) but when I checked them with the multimeter they were all at 3.32v (53.12v total). The BMS stats show 52.39 but the inverter showed 53.0v which agrees with the multimeter test.
Screenshot_20240919-201910.png
 
Update and question.
Here are the current stats. The BMS shows all of the batteries around 3.275v (52.4v total) but when I checked them with the multimeter they were all at 3.32v (53.12v total). The BMS stats show 52.39 but the inverter showed 53.0v which agrees with the multimeter test.
First, disconnect the battery from the inverter (if you have breaker, then it is easier), measure the battery voltage. If the JK BMS total voltage still doesn't match your multimeter, calibrate the BMS voltage via the app.

Then, reconnect the battery to inverter. Double check again the voltage at the inverter and the BMS.
 
Hi Ashley. I calibrated the BMS. Now they show the same. Thanks for that. On another thread you mentioned that a cell would be considered 95% if the cell was at 3.45v. here mine shows 98% with the cells around 3.315v.

Suprdav

Screenshot_20240920-192811.png
 
Hi Ashley. I calibrated the BMS. Now they show the same. Thanks for that. On another thread you mentioned that a cell would be considered 95% if the cell was at 3.45v. here mine shows 98% with the cells around 3.315v.

Suprdav

View attachment 245258
Ignore the SOC%. JKBMS has inaccurate shunt reading/calculation. You can read on on the other thread.
You will need to rely on the pack voltage to determine the actual SOC.
 