Zwy
Solar Wizard
From what I can gather from your posts, is you can't set parameters on your Daly BMS? Mine is a 250A 24V 8S Smart BMS with fan, common port, way oversized for the charging amps and discharging amps I intend to run thru it.GW without BMS charging fine, at 27.1v on GW monitor, 26.68 on battery ISDT meter.
One thing when testing the BMS that I didn't think of is that I have a different battery meter's shunt between the out wire for the BMS to the GW.
Could this be the problem? I think I'll test it later if the current charge goes up to top balance... was set at 28.2... thinking of setting 29v on the GW as it's charging nice and slow as the clouds come and go... I didn't think of the shunt before. Can't remember, but I think I did check the negative wire out of the battery to the shunt before with the same results... have to see if I wrote that down.
It is possible you're hitting the max charging amps your BMS can handle, what model do you have?
Second, it almost seems you are setting max charge voltage on the GW higher than the BMS max charge voltage. BMS should be at 3.65V per cell times 8 cells = 29.2V
The GW should be set lower than the BMS, my GW is set for 28.4V= 3.55V times 8 cells.
Are you certain you're setting this up backwards concerning max V for each component? From what you posted above,
"It's common port, so fixed settings ~30v high cutoff and 17.6v? low cutoff? I don't have it here at the computer, but it's lower than the batteries...So low end shouldn't have been a problem, just the high, as the fluctuating voltage that shows up on the GW monitor screen can go low below 25, usually 25.5, but I did see it today go lower for a moment on discharge, while the high charge can go over 31 if not set to 27v or lower"
If indeed you have run the GW over 31V, then it is quite possible to have cell damage. That would be 3.875V per cell.
Set BMS to max charging voltage 29.2V, and max cell voltage to 3.65V
Set GW to 28.4V max charging voltage.
Then see what occurs. And what is the BMS rated for charging amps? And what is your PV VOC again?