extremetinting New Member Joined Jan 23, 2020 Messages 6 Apr 12, 2020 #1 how many renogy 300 watt panels can i use with my lv 5kva-48v
Supervstech Administrator Staff member Moderator Joined Sep 21, 2019 Messages 11,782 Location Belmont, NC Apr 12, 2020 #2 It depends on your needs... battery size, loads, panel area available...
extremetinting New Member Joined Jan 23, 2020 Messages 6 Apr 12, 2020 #3 Supervstech said: It depends on your needs... battery size, loads, panel area available... Click to expand... have two 24volt battleborns 1400 load and 4 300 watt renogy panels wasn't sure if i should get 4 more for the mppt split faze
Supervstech said: It depends on your needs... battery size, loads, panel area available... Click to expand... have two 24volt battleborns 1400 load and 4 300 watt renogy panels wasn't sure if i should get 4 more for the mppt split faze
M MichaelK Solar Wizard Joined Mar 21, 2020 Messages 3,321 Location Sierra Nevada Foothills Apr 12, 2020 #4 I have 15. Decided it wasn't enough, and I'm in the process of adding a few thousand more watts.
extremetinting New Member Joined Jan 23, 2020 Messages 6 Apr 13, 2020 #5 MichaelK said: I have 15. Decided it wasn't enough, and I'm in the process of adding a few thousand more watts. Click to expand... thanks
MichaelK said: I have 15. Decided it wasn't enough, and I'm in the process of adding a few thousand more watts. Click to expand... thanks
Supervstech Administrator Staff member Moderator Joined Sep 21, 2019 Messages 11,782 Location Belmont, NC Apr 13, 2020 #6 extremetinting said: have two 24volt battleborns 1400 load and 4 300 watt renogy panels wasn't sure if i should get 4 more for the mppt split faze Click to expand... This states your equipment, but not your usage needs. What, and for how long will you be powering?
extremetinting said: have two 24volt battleborns 1400 load and 4 300 watt renogy panels wasn't sure if i should get 4 more for the mppt split faze Click to expand... This states your equipment, but not your usage needs. What, and for how long will you be powering?
extremetinting New Member Joined Jan 23, 2020 Messages 6 Apr 14, 2020 #7 Supervstech said: This states your equipment, but not your usage needs. What, and for how long will you be powering? Click to expand... garage lights 110 pool pump one couple chargers total about 1300 watts only about 7 hours a day
Supervstech said: This states your equipment, but not your usage needs. What, and for how long will you be powering? Click to expand... garage lights 110 pool pump one couple chargers total about 1300 watts only about 7 hours a day
Supervstech Administrator Staff member Moderator Joined Sep 21, 2019 Messages 11,782 Location Belmont, NC Apr 14, 2020 #8 Ok, 1300 x 7 is 9100Wh. You have 4 panels totaling 1200W, average daylight hours is 5, so you need 2 more panels to cover the load... almost... I would recommend 4 more.
Ok, 1300 x 7 is 9100Wh. You have 4 panels totaling 1200W, average daylight hours is 5, so you need 2 more panels to cover the load... almost... I would recommend 4 more.
Supervstech Administrator Staff member Moderator Joined Sep 21, 2019 Messages 11,782 Location Belmont, NC Apr 14, 2020 #9 You also need more battery if the hours are after dark... 2400Wh battery, will not feed 9100Wh of load...
You also need more battery if the hours are after dark... 2400Wh battery, will not feed 9100Wh of load...
P Ped Solar Enthusiast Joined Nov 4, 2019 Messages 754 Apr 14, 2020 #10 Pool pump probably doesn't run in winter. 9100wh total equals 6kwh through night. Turn pool pump off at night and it should be fine. 4 hours in winter, 8 hours in summer
Pool pump probably doesn't run in winter. 9100wh total equals 6kwh through night. Turn pool pump off at night and it should be fine. 4 hours in winter, 8 hours in summer
Supervstech Administrator Staff member Moderator Joined Sep 21, 2019 Messages 11,782 Location Belmont, NC Apr 14, 2020 #11 Ped said: Pool pump probably doesn't run in winter. 9100wh total equals 6kwh through night. Turn pool pump off at night and it should be fine. 4 hours in winter, 8 hours in summer Click to expand... Still... 6100Wh isn’t coming out of a 2400Wh battery...
Ped said: Pool pump probably doesn't run in winter. 9100wh total equals 6kwh through night. Turn pool pump off at night and it should be fine. 4 hours in winter, 8 hours in summer Click to expand... Still... 6100Wh isn’t coming out of a 2400Wh battery...
tictag Off-Grid Enthusiast Joined Dec 31, 2019 Messages 1,930 Location UK Apr 16, 2020 #12 extremetinting said: how many renogy 300 watt panels can i use with my lv 5kva-48v Click to expand... Assuming that you have the LV5048 model, you can connect up to 8,000W PV to it, or 26 300W panels (8,000W / 300W = 26).
extremetinting said: how many renogy 300 watt panels can i use with my lv 5kva-48v Click to expand... Assuming that you have the LV5048 model, you can connect up to 8,000W PV to it, or 26 300W panels (8,000W / 300W = 26).