I have had a generator inlet on the exterior of my home for several years, which I use in conjunction with a gasoline generator and an interlock switch at the main panel. I have a new Ecoflow Delta Ultra and I am adding a second inlet inside of my garage.
I plan to use a manual transfer switch to change the connection from the exterior inlet to the interior inlet. Both the generator and the Ecoflow have floating neutrals and therefore not considered “separately derived systems”. I rely on the main panel to provide my bonded neutral.
My question is, can I use a Double Pole Double Throw switch for this purpose such as https://www.amazon.com/Upgraded-Generator-General-Duty-120V-240V-100A/dp/B0D73TND4W and then tie all of the neutrals together inside the switch?
Or do I need a Triple Pole Double Throw switch like this, which will switch the neutrals? https://www.amazon.com/Siemens-DTGNF323R-100-Amp-240-volt-Non-Fused/dp/B00TEADJ0A
I’d prefer the first option because it is 25% of the price, but I believe it will result in the not in use inlet carrying current on the neutral.
Of course, 99.99% of the time, both inlets will be electrically disconnected by way of the interlock. My concern is only for when one of the inlets is energized.
I plan to use a manual transfer switch to change the connection from the exterior inlet to the interior inlet. Both the generator and the Ecoflow have floating neutrals and therefore not considered “separately derived systems”. I rely on the main panel to provide my bonded neutral.
My question is, can I use a Double Pole Double Throw switch for this purpose such as https://www.amazon.com/Upgraded-Generator-General-Duty-120V-240V-100A/dp/B0D73TND4W and then tie all of the neutrals together inside the switch?
Or do I need a Triple Pole Double Throw switch like this, which will switch the neutrals? https://www.amazon.com/Siemens-DTGNF323R-100-Amp-240-volt-Non-Fused/dp/B00TEADJ0A
I’d prefer the first option because it is 25% of the price, but I believe it will result in the not in use inlet carrying current on the neutral.
Of course, 99.99% of the time, both inlets will be electrically disconnected by way of the interlock. My concern is only for when one of the inlets is energized.