CostaRicaG
New Member
Newer to Solar. My system is 48 volt. 8 batteries in 2 strings of 4x12. AGM 150AH.
I charge up to 100% and as soon as PV off, they drop within 30seconds to about 75% charged.
I separated the two strings, and same results, so assuming that 1of 4 on each string is bad.
Voltage and amps on each battery, all 8 test normally.
I have a load battery tester and hoped it would be very clear in finding the issue.
Under load test, 6 batteries do test at 11.0-11.2 on the tester screen above. The other 2, one from each string, do test a little bit lower at 10.8 on this screen. Not a big difference.
Would you consider this proof of the bad batteries?
They test so close. No hot terminals. Any other wisdom to share?
I charge up to 100% and as soon as PV off, they drop within 30seconds to about 75% charged.
I separated the two strings, and same results, so assuming that 1of 4 on each string is bad.
Voltage and amps on each battery, all 8 test normally.
I have a load battery tester and hoped it would be very clear in finding the issue.
Under load test, 6 batteries do test at 11.0-11.2 on the tester screen above. The other 2, one from each string, do test a little bit lower at 10.8 on this screen. Not a big difference.
Would you consider this proof of the bad batteries?
They test so close. No hot terminals. Any other wisdom to share?