Thanks, it's a Daly 8s, 100A separate port. I also have to connect input from solar panels. If I tied the ports together won't it overload the charge port as it can only 50a max?I am not following your question. Could you provide a diagram and specific part numbers?
In general, a separate port BMS is best suited to situations where the charge and load are separated. With an inverter/charger you will probably have to tie the charge and discharge ports of the BMS together and feed it to the inverter/charger.
Does anyone know what the '50A Charge limit' on the Daly BMS means?However, you may have a problem if the combined charge current of the Inverter/Charge and SCC is greater than the 50A limit of the BMS. Can you set the inverter/charger to limit the charge current?
Just checked the inverter charger and it outputs be 10 and 70amps, would like to know if connected to the load port of the BMS, will it charge the batteries?Does anyone know what the '50A Charge limit' on the Daly BMS means?
Does it mean if you exceed 50 amps it will damage the unit?
**OR**
Does it mean the BMS will limit the charge current to 50 Amps?
**OR**
Does it mean it will detect an error and shut off charging if it goes above 50 Amps?
@Will Prowse used a lot of Daly BMSs back before we got so many options..... I hope he might know.
Since I am not a Daly expert I can't say for sure, but it would be very odd if it worked that way. If it did, what is the point of having a separate charge port?Would like to know if connected to the load port of the BMS, will it charge the batteries?
Thought so too. I've however contacted the store I bought the BMS, waiting to hear back. Grrr!! Should have just bought a common port.Since I am not a Daly expert I can't say for sure, but it would be very odd if it worked that way. If it did, what is the point of having a separate charge port?
Thanks, it's a Daly 8s, 100A separate port. I also have to connect input from solar panels. If I tied the ports together won't it overload the charge port as it can only 50a max?
Is it a separate port BMSI've been running charge current through p- for monthes on my daly.
Not sure if I have overvoltage protection but it works.
yesIs it a separate port BMS
Interesting.I've been running charge current through p- for monthes on my daly.
Not sure if I have overvoltage protection but it works.
Does anyone know what the '50A Charge limit' on the Daly BMS means?
Does it mean if you exceed 50 amps it will damage the unit?
**OR**
Does it mean the BMS will limit the charge current to 50 Amps?
**OR**
Does it mean it will detect an error and shut off charging if it goes above 50 Amps?
@Will Prowse used a lot of Daly BMSs back before we got so many options..... I hope he might know.
Over current protection is achieved by disconnect like a breaker. To reset a Daly bms you bridge b- to c- or p- I think it can also be achieved by disconnecting the balance leadsI have not used the Daly either so take my perspective as conjecture as well, but I have a vague impression none of the BMS' commonly used here (Daly, Ant, JBD, Chargery, SBMS) are capable of current limiting. I believe most of the FET based BMS' advertise overcurrent protection. So my guess is option 3: detect an error and shutoff charging or maybe shutoff all current in both directions I don't know.
This is an area I would like to learn more about, what is meant by overcurrent protection, how does it work, and is it designed to protect the system on a semi-regular basis, or is more of a catastrophic failure feature.
Also, as I learned more about Victron's guidance RE: the battery protect, I'm wondering if some of that same advice could/should apply to FET based BMS as well. The two things you don't want to do with the battery protect (as far as I understand) is (1) use it bidirectionally, and (2) use it to switch large loads with capacitors on the input side of the load (most commonly an inverter). This second point is what's got me thinking, because apparently failure due to this second mode is often quite slow, so it wouldn't be easily diagnosed or identified. This is just pure speculation, from someone not knowledgeable enough about electronics to be a competent speculator, so don't read into this too much. Something to ponder though.
It appears that you can put a reverse current through FETs in the BMS. (That is the way some of the hybred port BMS's seem to work.) You can get away with this for lower currents but if you tried to charge through the discharge port at a high amperage, things could get dicey. Either way, the BMS is operating in an unspecified way so knowing what level of current is 'safe' is very difficult. @BiduleOhm could probably add some detail here. He seems to have a strong understanding of analog circuit design and the various components. He reacted pretty negatively when we discovered a hybrid-port BMS that worked that way. (This is similar to running current backwards through the FETs of a Victron Battery Protect that @Will Prowse did in one of his builds. The build worked but Victron was adamant that it was a fire danger and was a completely unsupported configuration of the product. Consequently, Will changed the design.)
Also, if possible, set the inverter charger to something lower than the 60Amp charge current it is capable of. I would be leery of running 60A back-current through FETs rated at 100A forward current.