Inverter First Power on Checklist

sabo

New Member
Joined
May 26, 2021
Messages
67
Location
Sunny So Cal
I am looking for a checklist to review prior to flipping the switch on my Solar Disconnect Switch for the first time. I am looking to check my work so I can see if I am making any mistakes that may cause damage to my inverter. I searched the forum and on Google but only found this:

Off Grid Checklist

My system is battery less and currently no AC input or output connected yet.
Any suggestions or recommendations?

Thanks
 
Without knowing your setup other than no battery or grid AC in /out. It is hard to give advice.

Your manual should tell you the correct sequence for provisioning your system. The sequence from your link is a good overview of the subject but your manual takes precedence.
 
The instruction sheet for my camp lists:

Step 1: Turn on battery breaker
Step 2: Press and hold precharge button for 10sec
Step 3: Turn on inverter switch
Step 4: Turn on PV breaker
 
Polarity and voltage. Check with DMM.
Confirm voltage is what was expected, and within inverter limits.
Make sure you calculated PV panels Voc for cold weather and that also is within limits - otherwise it might operated until winter, then die.

Batteryless, you say. So Red Neck's precharge instructions don't apply (they are most important for lithium.)

Connect ground wire solar panel frames back to the system, and ground that to earth. People get AC shocks from undamaged systems, can get DC shocks if there is damage.
 
I screw that up all the time trying to remember the skinny peg goes in the fat housing and vise versa. ?
Now I am trying to figure out If or how this matters because hot will be hot all the way from the panels to the inverter but my cable colors may not be the same color all the way from the panel to the inverter. :(
 
Polarity and voltage. Check with DMM.
Confirm voltage is what was expected, and within inverter limits.
Make sure you calculated PV panels Voc for cold weather and that also is within limits - otherwise it might operated until winter, then die.

Batteryless, you say. So Red Neck's precharge instructions don't apply (they are most important for lithium.)

Connect ground wire solar panel frames back to the system, and ground that to earth. People get AC shocks from undamaged systems, can get DC shocks if there is damage.
Good to know, I thought I only had to ground to a ground rod near the panel mount.
 
I use colors for wire in conduit from inverter to junction box. Just black PV wire with MC3/4 connectors outside that.
Double-check polarity before closing switch to inverter (some but maybe not all have diode to clamp reverse polarity.)

When connecting MC connectors to something not visibly open-circuit, I use DMM to ensure it is open. Voltage starts out showing but decays as capacitance charges. If actually connecting to a short or parallel to a string of different voltage, DMM shows steady voltage.

As soon as you stick a DMM probe inside the touch-safe MC connector, you've got a non-touch-safe pin offering exposed hazardous voltage. Make or buy un-keyed MC to shrouded banana test leads?
 
Good to know, I thought I only had to ground to a ground rod near the panel mount.

Definitely not. If short from PV+ to frame, even grounding frame with a (25 ohm connection to earth) ground rod, you could get a shock. And earthworms will be annoyed.

Usually, ground wire lets a fuse/breaker trip. Generally not with PV, but it pulls voltage low. Ground wire ampacity should be 1.56x array ISC, as should current-carrying home-run conductor.

You'll find tales here of people being shocked by unconnected PV terminals of inverter, by panel frames, a dog who didn't like to climb steps of RV.

DC isn't as dangerous as AC (I recently had a close call at work), but if you have high voltage strings it is still a hazard.
 
"20 250w San Tan used panels"
Trina, I think.
At one point, Trina had leakage to frames and did a recall. I would think they would not let recalled panels reach the market, but all the more reason to ground frames.

"30.3 * 9 = 272 Volts"
Not "SELV" safe extra low voltage!

Proper grounding per NEC, a panel can be removed while maintaining ground to others. Either a clip that screws onto ground wire and has star washer to bite through oxide in aluminum PV panel frame, or something like WEEB hardware that bites between frame and rails.
 
"20 250w San Tan used panels"
Trina, I think.
At one point, Trina had leakage to frames and did a recall. I would think they would not let recalled panels reach the market, but all the more reason to ground frames.

"30.3 * 9 = 272 Volts"
Not "SELV" safe extra low voltage!

Proper grounding per NEC, a panel can be removed while maintaining ground to others. Either a clip that screws onto ground wire and has star washer to bite through oxide in aluminum PV panel frame, or something like WEEB hardware that bites between frame and rails.
Yes Trina
 
Now I am trying to figure out If or how this matters because hot will be hot all the way from the panels to the inverter but my cable colors may not be the same color all the way from the panel to the inverter. :(
It matters when you forget which wire is which and get the wrong end on a wire and now you've got the wrong polarity.

Or you end up with 3 males and 1 female and the relationship lists as "Complicated". ?
 
I use colors for wire in conduit from inverter to junction box. Just black PV wire with MC3/4 connectors outside that.
Double-check polarity before closing switch to inverter (some but maybe not all have diode to clamp reverse polarity.)

When connecting MC connectors to something not visibly open-circuit, I use DMM to ensure it is open. Voltage starts out showing but decays as capacitance charges. If actually connecting to a short or parallel to a string of different voltage, DMM shows steady voltage.

As soon as you stick a DMM probe inside the touch-safe MC connector, you've got a non-touch-safe pin offering exposed hazardous voltage. Make or buy un-keyed MC to shrouded banana test leads?
Can you link to an example of "un-keyed MC to shrouded banana test leads" I googled but am not sure if the results are truly what I searched for. I had a hard time getting the small pins on my multimeter to stay in contact with the inside of the MC4 connector.

Mutli Meter
 
MC4 banana test leads



I should buy myself a set before I succeed in killing myself more thoroughly.
I even have some sort of an Amazon coupon from work, enough to buy those inexpensive ones.

Both of those appear to have latches on MC4. Maybe not a big deal with the tool (I'm still using my fingers), or could be cut off.

I like that the male banana in Amazon picture has plastic tip. I've got some others I'm using everywhere (cost $40 for kit of 70 stackable banana, 5 colors) and what I don't like is that exposed metal end is only recessed a couple mm. I think I could come in contact if not careful.
 

At $19, a very low cost DMM.

Cheap meters aren't recommended for working on line voltages (because they don't have a fuse good enough to interrupt fault currents), but since this one is clamp current only, maybe not such a problem. Most of us have Fluke, maybe others.

That meter is AC amps only. You may find clamp DC handy. I selected Harbor Freight Ames 1000A meter because it can read inverter battery current, automotive starting current, also PV strings with 0.01A resolution. Most of the meters, including most Fluke, only have 0.1A resolution.

 
At $19, a very low cost DMM.

Cheap meters aren't recommended for working on line voltages (because they don't have a fuse good enough to interrupt fault currents), but since this one is clamp current only, maybe not such a problem. Most of us have Fluke, maybe others.

That meter is AC amps only. You may find clamp DC handy. I selected Harbor Freight Ames 1000A meter because it can read inverter battery current, automotive starting current, also PV strings with 0.01A resolution. Most of the meters, including most Fluke, only have 0.1A resolution.

Thanks for the recommendation I think I will pick one up.
 
Polarity and voltage. Check with DMM.
Confirm voltage is what was expected, and within inverter limits.
Make sure you calculated PV panels Voc for cold weather and that also is within limits - otherwise it might operated until winter, then die.

Batteryless, you say. So Red Neck's precharge instructions don't apply (they are most important for lithium.)

Connect ground wire solar panel frames back to the system, and ground that to earth. People get AC shocks from undamaged systems, can get DC shocks if there is damage.
The ground wire coming into the System from the panels, what should that be grounded upon? The Subpanel attached to the inverter output?
 