diy solar

diy solar

Is my wiring sound

I personally don't use fuses unless I have to. Instead I like these as it can be reset and comes in lots of different amp ratings. get from amazon

ANJOSHI Circuit Breaker 150amp 50A-300A with Manual Reset Home Solar System Fuse Holder for Car Audio and Amps Protection 12V-24V DC Reset Fuse Inverter Replace Fuses​

 
I personally don't use fuses unless I have to. Instead I like these as it can be reset and comes in lots of different amp ratings. get from amazon

ANJOSHI Circuit Breaker 150amp 50A-300A with Manual Reset Home Solar System Fuse Holder for Car Audio and Amps Protection 12V-24V DC Reset Fuse Inverter Replace Fuses​



And I wouldn't trust my house or vehicle with that thing unless it has UL (or equivalent) listing.
To receive that it would have been tested for current carrying, ability to interrupt overloads, and ability to interrupt high short-circuit current.

The following (content and grammar) do little to instill confidence:

"
Please Note:
1. Please correctly push the button to avoid damage the Circuit Breaker.
2. Please order and use the Circuit Breaker with right work temperature, to avoid it is too heat and stop work.
"
 
I

And I wouldn't trust my house or vehicle with that thing unless it has UL (or equivalent) listing.
To receive that it would have been tested for current carrying, ability to interrupt overloads, and ability to interrupt high short-circuit current.

The following (content and grammar) do little to instill confidence:

"
Please Note:
1. Please correctly push the button to avoid damage the Circuit Breaker.
2. Please order and use the Circuit Breaker with right work temperature, to avoid it is too heat and stop work.
"
Have used breakers like that many times on other 12v application without any problems, I don't think I have ever see a UL listing on any.
I first saw them used in the inverter compartment on a motorhome.

I just looked these are SAE and UL listed and comes in lots of amp ratings

T Tocas 100 Amp Circuit Breaker with Manual Reset, 12V- 48VDC, Waterproof (100A)​

 
Last edited:
I

Have used breakers like that many times on other 12v application without any problems, I don't think I have ever see a UL listing on any.
I first saw them used in the inverter compartment on a motorhome.

The UL rating of course isn't required for a vehicle. But it is a guarantee of performance to certain specs, which seems to be completely lacking with many of these sources.

Some may work. We see some of that style from Eaton and Blue Sea. Some forum members have had some of that style trip way below their rating; some sources don't meet claimed specifications. From Blue Sea, highest rating I see is 200A. So with the Amazon listing claiming up to 300A I question whether any are good for that much current.


"
Interrupt Capacity
information.png
5000A @ 12V
3000A @ 24V
1500A @ 42V
"

This shows the issue of interrupting a short-circuit current. A car battery can deliver about 3000A. Two 12V car batteries in series (starting circuit for some diesel trucks) would be 3000A @ 24V, the limit of what this breaker can handle. I believe a 100 Ah 12V lithium battery exceeds the breaker's ratings.

I would select a fuse or breaker with ratings sufficient for the load and the battery's short-circuit capability. From a trustworthy source and/or with lab certifications.
 
I would select a fuse or breaker with ratings sufficient for the load and the battery's short-circuit capability. From a trustworthy source and/or with lab certifications.
I would agree with fuse/breaker rating sufficient for the load(s)
In his drawing he over sizes the fuse on both solar charger by 10 amps, is that a standard practice?
Also I see he only has a 2000 watt inverter 2000/12vdc= 167 amps.
The problem I see is a 400 amp fuse with only a 300 amp switch and from the chart I look at by altE 2/0 only handles 195 amps.
IMO the weak link always needs to be the fuse/breaker but never a switch or wire.
 
I would agree with fuse/breaker rating sufficient for the load(s)
In his drawing he over sizes the fuse on both solar charger by 10 amps, is that a standard practice?
Also I see he only has a 2000 watt inverter 2000/12vdc= 167 amps.
The problem I see is a 400 amp fuse with only a 300 amp switch and from the chart I look at by altE 2/0 only handles 195 amps.
IMO the weak link always needs to be the fuse/breaker but never a switch or wire.
A fuse/breaker is meant to protect the wire. If you have a 40A load you select a wire that can safely handle 40A. Then you select a fuse/breaker size that is between the expected max load your selected wire is going to handle and the max amps that the wire can actually handle. Since the first SCC can put out 50A, you do not want a 50A fuse or it will likely blow during normal usage. So picking a higher amp fuse is correct. Since a single, quality 6AWG wire can easily handle more than 60A, the 60A fuse is a good choice. It protects the wire while not causing nuisance trips.

Regarding the 400A fuse, that has been covered by several earlier posts already.
 
I would agree with fuse/breaker rating sufficient for the load(s)
In his drawing he over sizes the fuse on both solar charger by 10 amps, is that a standard practice?

30 amp charge controller with 40 amp fuse, 50 amp charge controller with 60 amp fuse.
The 6 gauge wire on each is sufficient.

We normally size the fuse/breaker 25% higher than max continuous current, to avoid nuisance trips. So I might have used 70A fuse for 50A SCC.
Some loads might occasionally draw higher current, but charge controllers measure and are programmed to hit an exact value.
Thermal fuses/breaker trip at different currents depending on ambient temperature.
Some breakers are magnetic/hydraulic. Midnight says theirs can be run continuously at 100%

Also I see he only has a 2000 watt inverter 2000/12vdc= 167 amps.
The problem I see is a 400 amp fuse with only a 300 amp switch and from the chart I look at by altE 2/0 only handles 195 amps.
IMO the weak link always needs to be the fuse/breaker but never a switch or wire.

Yes, want the fuse to be weak link not the wire.
2/0 with 90 degree insulation, single conductor in free air is rated 300A. If 105 degree insulation the figure is something higher, but I'm not finding the charts for it right now.

Blowing fuses is inconvenient. They (and wires) should be sized so they never trip except if a short circuit.
Breakers tripping can cause wires to overheat, damaging insulation if this happens many times. The breaker also can only handle a limited number of disconnects under overload, sometimes only 1 or 2 in the case of a short circuit.
Something like stalled motors you would like to detect and shut off before that happens. Also better for the motor's windings that way.
 
In that case redundant batteries is good. Do they have a Bluetooth app or something to check on them, so you can tell if one fails? That way, you'll know to remove it for repair, and to reduce the load you apply so remaining two won't be subject to excess current.

Two or four batteries is easy to parallel for balanced current draw. Since you have three, good to not simply parallel them with short cables but instead use 3 matched length cables on each of positive/negative. Long individual wires and short single wire after combining would help. If your inverter might draw more than what two batteries/BMS can supply, you want it evenly distributed.
Hedges, (or anyone else) .....I need some newb clarification on your statement to "use 3 matched length cables on each positive/negative." I have attached a picture of my diagram of what I had planned for installing my 3 batteries and another diagram of what I believe you are suggesting to do. If you look at my diagram I have added a wire from battery 1 positive to battery 3 positive and then added a wire from battery 1 negative to battery 3 negative. Is this what you are saying to do? Thanks in advance!
 

Attachments

  • IMG_0555.jpg
    IMG_0555.jpg
    80 KB · Views: 5
No, I don't think that is perfectly matched.
Something like the the diagram on the right works for 2 batteries.
For four batteries there is a slightly more complicated scheme to accomplish similar.

For 3 batteries, you might connect positive terminals of all three batteries to a fuse, using a 1' wire from each battery.
You might connect negative terminal to a shunt (or a busbar, or just a bolt) from all three batteries using a 1' wire from each battery.
That way, current from each battery goes though exactly 2' of wire before joining the others.
(rather than having your inverter cable go to any one of the batteries directly.)

If I was stacking three ring terminals on a bolt I think I'd place them in order A,B,C for the positive terminal and C,B,A for the negative terminal so none of the batteries sees a different path length from the others. (maybe that is splitting hairs.)
 
No, I don't think that is perfectly matched.
Something like the the diagram on the right works for 2 batteries.
For four batteries there is a slightly more complicated scheme to accomplish similar.

For 3 batteries, you might connect positive terminals of all three batteries to a fuse, using a 1' wire from each battery.
You might connect negative terminal to a shunt (or a busbar, or just a bolt) from all three batteries using a 1' wire from each battery.
That way, current from each battery goes though exactly 2' of wire before joining the others.
(rather than having your inverter cable go to any one of the batteries directly.)

If I was stacking three ring terminals on a bolt I think I'd place them in order A,B,C for the positive terminal and C,B,A for the negative terminal so none of the batteries sees a different path length from the others. (maybe that is splitting hairs.)
Thanks for the explanation. I think I will get two 300 amp rated 4 post busbars and use exact same length wires for the battery to busbar connections and then 2 wires the same length for the busbar to inverter connections. (like the attachment). Would you recommend this strategy?
 

Attachments

  • IMG_0559.jpg
    IMG_0559.jpg
    51.7 KB · Views: 2
I cannot recall where i got this, just another possible solution.
View attachment 46889
Ok, I am going to pull the newb card again..... How can I apply this to a 3 battery bank? I was planning on wiring my bank like your diagrams' "suitable for most applications" until I read a post somewhere saying that for 3 batteries you should be careful with battery cable lengths and possibly use busbars to connect in parallel. It didn't sink in until Hedges post reinforced what is probably best practice for wiring 3 batteries in parallel. I am limited in space so 3 batteries is what I have to work with in my camper. I just want to do it right the first time which is why I am asking. Thanks for the response!
 
You may find the following resource helpful. It includes a great discussion about connecting batteries (and many other topics).

 
You may find the following resource helpful. It includes a great discussion about connecting batteries (and many other topics).

I have referenced this ebook from Victron multiple times and it is helpful. I guess my question was that I was set to wire my battery bank "diagonally" like the first illustration on page 18 of the book explains (for a 4 battery bank) but I read in a post that using busbars like the 4th illustration was better. Hedges seemed to suggest using the "posts" method was acceptable and I agree. I did not understand how I could implement the "Halfway" method on a 3 battery bank, though. I just wanted to know if I should abandon my plan of wiring my 3 battery bank diagonally and use the posts or busbars method instead? Are these two methods better in some way I don't know about?
 
Thanks for the explanation. I think I will get two 300 amp rated 4 post busbars and use exact same length wires for the battery to busbar connections and then 2 wires the same length for the busbar to inverter connections. (like the attachment). Would you recommend this strategy?

Getting there. I think I would move one inverter cable to opposite end of its busbar.
Might be OK to skip the busbar, just join the four ring terminals on one bolt.

Got fuses?
That could be 3 fuses, one per battery. Or one fuse for all three.
 