I'm just theorizing idk if its 40a or 80a. I dont know anything. I do know i got 80 amps going to my battery busbar from 10 panels all wired in paralell for 36v and 80a.
Sorry if this has been a bit of a learning curve for you! But, hey, if life were simple it would be boring! ;-)
As mentioned in my responses to your PMs, you need to find out from your battery manufacturer what their recommended charge rate limit is. C/10 is a 'safe' charge rate for most lead-acid batteries - yours could be C/5 or even C/2 which would mean you could throw 50A into it!
But if the answer is C/10 then the fact is your system as configured will fry your batteries. Boiling everything down, a 2,500W array will dump 104A into a 24V battery bank, meaning each of your 5 'legs' will receive 20.8A, which is twice the recommended limit for a C/10 rated battery (
and, funnily enough, exceeds your busbar terminal stud rating too...). It will absolutely work, your batteries will charge and everything will look good, until you eventually realise that your batteries are getting hot, water will begin electrolysis and produce a flammable mixture of oxygen and hydrogen, the water in the electrolyte will evaporate (if open) and/or build vapour pressure (if 'maintenance free') and potentially blow its protection valve, spilling out explosive gasses and corrosive acid...
And.....RELAX!
None of that is going to happen because you are going to:
- Determine the maximum charge limit as recommended by your battery manufacturer and
- Design your system so this is not exceeded
Tic tac said:
Yes. Lead-acid batteries generally speaking have a C/10 maximum charge rate (some AGMs allow up to C/5), which for your battery bank that's 80A (800AH / 10 = 80A). You should not regularly exceed this to avoid premature aging.
This is correct but requires context: a typical 800AH battery bank can be charged safely at 80A assuming a C/10 maximum charge rate. You don't have an 800AH battery bank, you have a 400AH at 24V battery bank.
Edit: Corrected typo.