lowering voltage drop with parallel conductor

xixxixxixxi

New Member
Joined
Mar 15, 2024
Messages
2
Location
wisconsin
I have a 500 foot run of 3 conductor 8 gauge copper. I only use 2 of the conductors and ground to connect my 240 volt 9.6 kv microinverter system to the main panel. My question is whether I could use the 3rd conductor to double up on one of the legs reducing voltage drop. I had people say I can't because of "imbalance" and it's probably against code, but does someone have an explanation of why it wouldn't work?
 
I didn't call you on it ;-)! It makes sense. I have no idea how it's run but ...

Southwire shows 11.51% 240v@40A #8 copper 500FT, reports 20A at 5.75%, so pretty much spot on. Takes it to 8.63% so still 21v vs 27v.

Not sure about code, don't know why it would be a problem as long as you have each conductor properly fused/breaker'ed.

OTOH If you replaced the cable with 500FT of (2/0)x3+1 URD Aluminum quadraplex direct burial. $3/ft = $1500 + trenching. 40A is 2.71%, 100A is 7%. Even better, and you would have some headroom. 4/0 would be ~$4/ft ($2000), drop it under 1% for 40A, and ~7% for 150A.

So 4/0 would put you under 4% 9.5v on 80A. I honesty think that would be a better target, though 2/0 would get you down under 7v at 40A.

500FT is a pretty long run. Is it really 500ft? Either way, #8 is decidedly sub-optimal.
 
Is there a reasonable reason to not do it? I can see it being a bit confusing to figure out what's going on if you weren't the installer but otherwise...
 
Is there a reasonable reason to not do it? I can see it being a bit confusing to figure out what's going on if you weren't the installer but otherwise...
I wouldn't recommend it.
But if someone was going to do it, they should follow the same rules for parallel conductors of the approved size.
All conductors of the circuit paralleled. (Not just one)
All conductors of the same size. (Not different sizes)
Parallel conductors are treated as a single conductor. (Connecting to the same place on both ends, and protected by one OCP device)
 
Thinking about safety, not code here. Would you want them on the same breaker or on separate breakers appropriate for the wire? (ie paralleling #12, would I want a 20 amp on each wire or both hooked to a 40? Thinking about this some more I can see this getting confusing very quickly.

What does code require for breakers when paralleling is allowed?
 
actually now that I think about it its 350 feet not 500. Interesting comments but still wondering whether there would there be any danger in wrecking my microinverters having 2 parallel wires for the one leg and only 1 for the other? I hate to have that 3rd wire in the ground not being used for anything if it could lower my voltage drop. The reason I'm concerned about the voltage drop is that my system severely limits itself on a sunny day due to the voltage rising to 263 on the microinverter side and 255 on the main panel side. My 9.6 kw system tops out at about 6 kw unless I hook up some large loads to drop the grid voltage.
 