Hi guys,
I was hoping to get a little feedback on my planned solar installation as it relates to load calcs and service panel sizing. I plan to install a 7.200 kW system (18 panels x 400 watts) with microinverters and have 2 questions:
1) Is my main panel adequate to support the planned PV output?
2) Why is the city asking me to add 40 amps to my residential load calc?
1) Is my main panel adequate to support the PV output?
Main service panel is an Eaton "solar ready" MBED2040PV125BF
bus = 225 amps
main breaker = 125 amps
Per the "120% rule" the maximum PV output the panel can support is:
((Busbar Rating (A) x 1.2) - Main Breaker Rating (A) )/1.25 = Max PV (A)
Max PV (A) = ((225 amp x 1.2) – 125 amp) / 1.25 = 116 amp
Max PV (kW) = 116 amp x 240 / 1000 = 27.84 kW
Since this is well beyond the planned system of 7.2 kW, I believe this is more than adequate and no derating is required etc. - could this be confirmed please?
As part of the project I also plan to install EV charger. When applying for a city permit, the city's load calculation form shows all of the standard entries by square footage, appliances max. of non-coincident loads etc. per NEC standards.
But at the very end of the form they have included a line labelled "40 amp back-feed protection for future PV system (solar panels) +40 Amps".
So they basically require 40 amps to be added to the standard load calculation to account for solar.
Does this really make sense? I did a fair amount of googling and nowhere else (other municipalities etc.) do I see any versions of the NEC load calcs that include this. I just don't get why the solar output (which is supply) needs to be counted as load?? I have a feeling this is not correct. Any thoughts/feedback would be appreciated.
Thanks
Dennis
bus = 225 amps
Thanks
Dennis