If your grid has that high voltage, you should contact your utility company.
There should be a transformer close to your home where they could adjust the ratio between input/output.
The nominal voltage should be 120 volt per split phase so 240 volt together. Your 2 x 133 = 266 volt.
That is almost 11% over the nominal voltage.
I found this document with some searching:
So it seems your 11% is way out of line.
Hence my suggestion to contact your utility company.
Not something you should adjust on your inverter IMO.
*UPDATE*
I just saw your location is not the USA so your local conditions might be different. Check with your local utility.