All batteries have different Peukert exponents. So what?Wait - what about the fact that lead-acid has a Peukert effect, whereas with LFP, there is practically none?
All batteries have different Peukert exponents. So what?Wait - what about the fact that lead-acid has a Peukert effect, whereas with LFP, there is practically none?
You bought up the Peukert effect as if it is something to be concerned with. So it is entirely reasonable to ask you why you think it is something to be concerned with.Instead of asking me, how about asking those who do know more about batteries than you or I do
So the concern you are expressing is for efficiency, not safety.If the voltage disparity is large enough, the LFP will be trying to recharge the lower-voltage lead-acid battery at the same time it is discharging. This is not efficient for one thing.
I have expressed the safety reason before as well. This was just an additional point because here there is apparently no concern for safety.So the concern you are expressing is for efficiency, not safety.
That is not true. There is no disregard for safety.I have expressed the safety reason before as well. This was just an additional point because here there is apparently no concern for safety.
It's not they are not welcome, it's they need explaining.My remarks about pesky little things like Peukert differences, are not welcome
Now that is a reasonable statement that you don't see any advantages and you perceive some disadvantages, namely a loss of high capacity, continued weight of lead, watering and maintenance of lead, and Puekert effect concerns. In my experience, first, as I perhaps did not explain well enough previously, my off-grid cabin had 330Ah @ 24v, of FLA. It was less than two years old, and while I can afford whatever I want, I am not inclined to toss it out when it has so much life in it. Others may feel differently. Rather, I was wishing to add capacity and also to get the advantages of Lifepo4, without ruining a perfectly good battery. So, I added 200Ah in parallel with the FLA, with a device (BBMS) that enables them to be joined the vast majority of the time but disconnected when the Lifepo4 is full and the controller charging, which allows the charging voltage to increase when it drops off so as to top off my FLA per normal parameters. When done charging the FLA, the voltages come back together and it again joins them. Since the FLA is only 165Ah in practical terms (limited to 50 percent discharge), this more than doubles my capacity. You expressed concern that somehow this loses the advantage of "high capacity" found with LifePo4. I am not sure how you would even come to anticipate that, but I am open to clarification if you wish. For me it is just the opposite in that I have higher capacity. With regard to the dreaded ol' Puekert effect, unlike when using solely FLA there is little voltage sag because the Lifepo4 in the mix discharges more rapidly most all of the time. Only if I were to have a very, very high amperage draw, or if I were to take my Lifepo4 very, very low would the FLA come to predominate and result in some significant FLA-style Puekert effect voltage sag you expressed concern about. To be clear, I don't experience that in regular use; rather, voltage remains quite stable. So, I get both higher capacity and no Puekert concerns, and while I could see that as a hypothetical concern, mixing them doesn't ruin those LiFePo4 characteristics at all in my experience. Additionally, the FLA stays nearly fully charged most of the time, and the trickle from the Lifepo4 overnight into the FLA is very minimal. No big energy loss due to that fear some express. Also I anticipate that trickle will only benefit the FLA in the long run. Addressing your other expressed concerns, it is true I still have to monitor the water in my FLA. That is a valid point based on my experience. However, since this is a stationary installation, the weight concern you expressed is of no import, but I understand the issue for mobile applications which is why in my vehicle based system I use solely LifePo4. In summary, of your worries about the LifePo4 advantages you fear would be lost, I can validate only the remaining higher weight and having to water the FLA occasionally. With regard to a loss or ruination of the LiFePo4 advantages high capacity, and of the small Puekert effect, these have simply not been born out by my experience. Now, in my special circumstance, I might add that I have additional advantages in that I am on the central plains and have a very good small wind turbine that works very well with my FLA. Such wind generators are in essence traditional alternators, which you may know cause havoc for Lifepo4 (at least without the additional circuitry of newer smarter alternators, I am told). In my circumstance, leaving lead in the circuit allows that lead to do all that it should vis a vis that turbine, dampening the effect of a variable voltage source. In fact it runs even better now because wind gusts do not push the voltage up as drastically with the lower resistance of the Lifepo4 (again, good riddance to significant Puekert effect). It essentially allows more room for that rapid charge of higher winds and results in much less braking because voltage doesn't spike.I'm confused as to why anyone would want to in the first place. I've watched several videos, and checked out the "BBMS" Whether or not it is safe, I don't see any advantages, and you are tossing out and ruining the advantages you get from LFP. Namely, high capacity with a light weight, no Peukert (which makes accurate monitoring of SOC possible), and no battery maintenance(watering, periodic equalization, etc.). Why have Lithium in the mix at all if you lose the advantages from it?
You are much better off tossing the lead and having a smaller Lithium battery than a larger hybrid imho. Or if you need the larger battery and can't afford to do it all in Lithium, do it all in lead.
My capacity statement was in regards to buying a bank that is all lfp, vs one that is physically the same size, but hybrid. Many installations have a space constraint. I do, and the switch to lfp tripled my usable capacity in the same space.Now that is a reasonable statement that you don't see any advantages and you perceive some disadvantages, namely a loss of high capacity, continued weight of lead, watering and maintenance of lead, and Puekert effect concerns. In my experience, first, as I perhaps did not explain well enough previously, my off-grid cabin had 330Ah @ 24v, of FLA. It was less than two years old, and while I can afford whatever I want, I am not inclined to toss it out when it has so much life in it. Others may feel differently. Rather, I was wishing to add capacity and also to get the advantages of Lifepo4, without ruining a perfectly good battery. So, I added 200Ah in parallel with the FLA, with a device (BBMS) that enables them to be joined the vast majority of the time but disconnected when the Lifepo4 is full and the controller charging, which allows the charging voltage to increase when it drops off so as to top off my FLA per normal parameters. When done charging the FLA, the voltages come back together and it again joins them. Since the FLA is only 165Ah in practical terms (limited to 50 percent discharge), this more than doubles my capacity. You expressed concern that somehow this loses the advantage of "high capacity" found with LifePo4. I am not sure how you would even come to anticipate that, but I am open to clarification if you wish. For me it is just the opposite in that I have higher capacity. With regard to the dreaded ol' Puekert effect, unlike when using solely FLA there is little voltage sag because the Lifepo4 in the mix discharges more rapidly most all of the time. Only if I were to have a very, very high amperage draw, or if I were to take my Lifepo4 very, very low would the FLA come to predominate and result in some significant FLA-style Puekert effect voltage sag you expressed concern about. To be clear, I don't experience that in regular use; rather, voltage remains quite stable. So, I get both higher capacity and no Puekert concerns, and while I could see that as a hypothetical concern, mixing them doesn't ruin those LiFePo4 characteristics at all in my experience. Additionally, the FLA stays nearly fully charged most of the time, and the trickle from the Lifepo4 overnight into the FLA is very minimal. No big energy loss due to that fear some express. Also I anticipate that trickle will only benefit the FLA in the long run. Addressing your other expressed concerns, it is true I still have to monitor the water in my FLA. That is a valid point based on my experience. However, since this is a stationary installation, the weight concern you expressed is of no import, but I understand the issue for mobile applications which is why in my vehicle based system I use solely LifePo4. In summary, of your worries about the LifePo4 advantages you fear would be lost, I can validate only the remaining higher weight and having to water the FLA occasionally. With regard to a loss or ruination of the LiFePo4 advantages high capacity, and of the small Puekert effect, these have simply not been born out by my experience. Now, in my special circumstance, I might add that I have additional advantages in that I am on the central plains and have a very good small wind turbine that works very well with my FLA. Such wind generators are in essence traditional alternators, which you may know cause havoc for Lifepo4 (at least without the additional circuitry of newer smarter alternators, I am told). In my circumstance, leaving lead in the circuit allows that lead to do all that it should vis a vis that turbine, dampening the effect of a variable voltage source. In fact it runs even better now because wind gusts do not push the voltage up as drastically with the lower resistance of the Lifepo4 (again, good riddance to significant Puekert effect). It essentially allows more room for that rapid charge of higher winds and results in much less braking because voltage doesn't spike.
I hope that explains how, in reality, it is true that a few advantages of an all LifePo4 battery are diminished with a hybrid system. Weight remains with lead in the mix, as does watering. But the other expressed concerns of losing capacity and keeping some effects of Puekert are either non existent or not a significant concern. And there are some advantages related to alternator charging, and keeping the lead you have in service until it's eventual death. I anticipate adding a smaller amount of lead when my FLA does eventually die for the reasons stated.
I hope this clears up the confusion for you. Of course, this setup may not be for all or even many, but for some significant lot of us it is ideal. In any such setup, the banks have to have proper over current protection devices (separately fused) to prevent malfunction of one causing any damage to the other.
I agree it's not a suitable solution in most circumstances.I'm confused as to why anyone would want to in the first place.
Appreciate what you're saying regarding capacity and space to store batteries. In my case, I already had the lead in my cabin's garage and some space for a bit of Lifepo4 was not hard to come by. I suppose if I were trying to increase capacity all within the same space it would not fit, adding an additional Lifepo4. Still, my capacity more than doubled and it just took a little more space in my garage. Had I replaced it all with LifePo4 then it would all have fit in my FLA space. Space requirements may be an issue in a particular case, just not in mine. Regarding SOC concerns, I don't have any. My Lifepo4 BMS shows it's SOC accurately, and I know the voltage of the system and where the lead is in relation to that until Lifepo4 is nearing depletion. The flatness of the Lifepo4 is beneficial of course in that my LA is largely preserved throughout use of the Lifepo4. So the sudden unexpected realization of LA depletion scenario is not a concern for me and hasn't occurred. I never depended on a shunt to know capacity remaining of my LA before anyway, so it's no different. Others may need that in their setup, granted. Forgetting battery watering sounds great. I do, in fact, experience that in my mobile system, just not at my cabin, so I appreciate what you're saying about giving up that task. I guess it's the price I pay for the overall benefits of a mixed system.My capacity statement was in regards to buying a bank that is all lfp, vs one that is physically the same size, but hybrid. Many installations have a space constraint. I do, and the switch to lfp tripled my usable capacity in the same space.
My issue with Puekert isn't what you discuss. Its that because of Puerkert it is practically impossible to know the state of charge of a LA battery. You _think_ you are using 50%(or whatever you think you use) of it. But without a whole lot of work and very sophisticated monitoring and regular capacity measurements and calibration, i promise you, you are wrong. With LFP knowing the SOC is easy, until you parallel a LA and screw that up. This is really the biggest issue for me . Its very real you might think you have 50% total capacity left, then all of the sudden your inverter turns off I would rather have a smaller battery and be certain what's left.
Regarding maintenance, you don't appreciate that yet. But i switched from FLA to LFP. I 100% ignore it now, except for an occasional glace at my SOC. Its been a year since i bothered with anything. I'll never go back. FLA is agonizing to tend to. But if you are used to it, you don't appreciate yet what you're missing.
If your boat burns down, and the inspectors see a hybrid-bank