An therein lies the crux of the matter. We are talking about systems that when fail will create enough heat to burn themselves into nothing along with all of the things around them until all of stored energy is gone.The answers so far aren’t the easiest to understand considering this post is in the beginners forum
Someday someone will provide something other than thier opinion about the Asymmetrical Fault Current we need to design for.
From hereHi, on a 24V system with 3000W inverter and 280ah battery, can I use a 300a MRBF terminal fuse or should I use a 250a Class T fuse. I prefer the MRBF but what to be safe without going over board
exactly, but where does beginner start and endThe answers so far aren’t the easiest to understand considering this post is in the beginners forum
Here is what I use - https://www.amazon.com/Midnite-Solar-MNEDC175-Panel-Breaker/dp/B00SGGVPTK
Not cheap but has 50,000 AIC rating and allows me to turn on/off my batteries easily.
any recommendations for a 1000A shunt and a contactor that would tolerate closing onto a short? ? i have wanted to *safely* test this for a while. the previous closest test i saw on this forum, someone used a decent length of like 6awg cable to provide a tempering reistance.Educated opinion or SWAG. I am going by the reported measured IR of LiFePO4 cells, 0.17 milli-ohm.
Measured fault current is what we need. But I don't think it will exceed the figure I'm using, so that is safe for designing to.
Anybody feel like shorting their battery through a 1000A shunt, maybe get 1V drop across it?
Scope trace could capture the waveform, current interrupted shortly thereafter by a fuse.
I've seen a reported measurement of 4000A for 100 Ah AGM.
My calculation for typical starting battery, based on cranking amps, is 3000A.
I feel good relying on 20,000A figure for LiFePO4 cells.
Only so many fuse types to consider, place your bet and take your chances.
internal resistance of pack, voltage, resistance of other componentsOK, that leads me to my next question. How do you calculate your AIC rating/need?
MRBF or class T
being exposed to concepts of ohm's law and battery pack internal resistance seem like good options.exactly, but where does beginner start and end
In a parallel bank that already has a Class T before the inverter, is ANL ok for each battery before the busbar?
any recommendations for a 1000A shunt and a contactor that would tolerate closing onto a short? ? i have wanted to *safely* test this for a while. the previous closest test i saw on this forum, someone used a decent length of like 6awg cable to provide a tempering reistance.
What's interesting about this subject is that you see very little about in builds on internet, youtube, etc. I bet you'd have a hard time finding a build/diagram that shows the use of Class T fuse or even MRBF for that matter. Only thing I see is about sizing fuse/breaker and if they do mention fuse it is ANL or MEGA. I wonder whyMRBF vs Class-T fuse,
i am also still grappling with this topic for LiFePO4 battery build.
the tentative conclusion for me is,
12V LFP? MRBF probably ok.
24V LFP? MRBF *maybe ok*
48V LFP? Class-T Definitely
the different cost in components is very important to me. class-t are generally almost 5-10x cost of MRBF. whether saving 30-50 usd per battery pack is worth the potentially reduced safety margin, i don't know. i want to use class-t on every individual pack, but the cost is indeed offputting.
many documents/designs may be based on lead acid and have not been updated, is the rationale i usually attributeI wonder why
No, what I've was lifepo4 builds!many documents/designs may be based on lead acid and have not been updated, is the rationale i usually attribute
i see, just to help clarify,No, what I've was lifepo4 builds!