Class T fuse or even MRBF for that matter. Only thing I see is about sizing fuse/breaker and if they do mention fuse it is ANL or MEGA.
To assist consideration, here is a table of the various fuse types and their Ampere Interrupt Capacity at various voltages.
The data is sourced from Blue Sea Systems, specifically the 250A type, or the highest possible rated alternative. Links in the name type.

Type​
MSRP USD​
AIC per USD​
AIC @ 14V DC​
AIC @ 32V DC​
AIC @ 48V DC​
AIC @ 125V DC​
3​
333​
1,000 A​
MAXI
7​
142​
1,000 A​
8​
250​
5,000 A​
2,000 A​
12​
166​
2,000 A​
MRBF
19​
263​
10,000 A​
5,000 A​
2,000 A​
ANL
30​
200​
6,000 A​
45​
444​
20,000 A​

"AIC per USD" is calculated using MSRP and the 32V DC AIC Rating or the Next Highest Voltage AIC Rating. For Class-T, the 125V DC AIC Rating was used. Its units are Amperes Interruptable Per USD.

The AIC per USD is for comparing AIC value of different fuse types. According to the respective MSRP listed, the Class-T fuse is more AIC amps per dollar than all the other fuse types offered on that site. This is using MSRP listed on Blue Sea Systems, which might not reflect real prices available. All MSRP prices rounded up to the next one.

Hope this helps somewhat. I also needed to see this table ?
 
OK, that leads me to my next question. How do you calculate your AIC rating/need?
To calculate AIC rating/need, divide the max cell voltage by the internal resistance in ohms to get amperes.

@Hedges mentioned 20,000 Amperes to be able to interrupt, but how to get to this number? 0.17 milliOhms was mentioned, and 3.65 Volts is the max LiFePO4 cell voltage. dividing 3.65 V by 0.00017 Ohm equals ~21,470 Amperes or about 20,000 Amperes.

if a given LiFePO4 cell had internal resistance of 1 milliOhm then the AIC needed would be 3.65 V / 0.001 Ohm equals 3650 Ampere or about 4000A.


this was my reference for how to know to divide voltage by ohms to get amperes
1664105667859.png


hope this helps!

one tip, not all internal resistance meters can accurately measure internal resistance in Ohms on large capacity cells like 300Ah cells and alternate methods can be used to get more accurate data for those kind of cells.
 
To calculate AIC rating/need, divide the max cell voltage by the internal resistance in ohms to get amperes.

@Hedges mentioned 20,000 Amperes to be able to interrupt, but how to get to this number? 0.17 milliOhms was mentioned, and 3.65 Volts is the max LiFePO4 cell voltage. dividing 3.65 V by 0.00017 Ohm equals ~21,470 Amperes or about 20,000 Amperes.

if a given LiFePO4 cell had internal resistance of 1 milliOhm then the AIC needed would be 3.65 V / 0.001 Ohm equals 3650 Ampere or about 4000A.


this was my reference for how to know to divide voltage by ohms to get amperes
View attachment 113439


hope this helps!

one tip, not all internal resistance meters can accurately measure internal resistance in Ohms on large capacity cells like 300Ah cells and alternate methods can be used to get more accurate data for those kind of cells.
Nice explanation, really helps.
 
personally my current primary fuse plan for 12v and 24v LiFePO4 batteries is one MRBF mounted on each battery positive, in addition to one Class-T fuse upstream of all paralleled batteries, and sure to physically protect the inbetween wiring.
Since I only have one 280ah 24v battery, I would think in my case adding MRBF and Class-T fuse would not make sense. I do think that a 250a Class-T fuse would be a good idea. Maybe not absolutely necessary but certainly won't hurt.

Again thank you to all, I appreciate the learning and help! ?
 
With a single battery of 280Ah 24V (8 cells series), a 250A Class-T fuse seems like a generally good idea (y)
 
What's interesting about this subject is that you see very little about in builds on internet, youtube, etc. I bet you'd have a hard time finding a build/diagram that shows the use of Class T fuse or even MRBF for that matter. Only thing I see is about sizing fuse/breaker and if they do mention fuse it is ANL or MEGA. I wonder why

I've mentioned it a few times in various posts here on the forum. I explained several times what size to use. I also made the diagram that is now used with the JK BMS showing class T fuses when paralleling packs. I've always said to use class T fuses with lithium, and if you're at 48V, there are few other choices.
 
@Will Prowse - how about a video testing lithium max current and fuses, maybe some of the shittier breakers too

What happens if a Lifepo4 battery is shorted out? What is the max current? Is it 20,000 amps?

Do the various fuse types protect against a direct short. What does it look like if they don’t?

It would be important learning for folks, educational, interesting to see and has the potential to be quite entertaining ?

Could be a whole series, similar to the “will it blend” old skool you tube
 
@Will Prowse - how about a video testing lithium max current and fuses, maybe some of the shittier breakers too

What happens if a Lifepo4 battery is shorted out? What is the max current? Is it 20,000 amps?

Do the various fuse types protect against a direct short. What does it look like if they don’t?

It would be important learning for folks, educational, interesting to see and has the potential to be quite entertaining ?

Could be a whole series, similar to the “will it blend” old skool you tube

This publication has a graph of a shorted 160Ah 3.2V LiFePO4 cell:

The-plot-of-current-and-temperature-during-short-circuit-of-LiFePO4-160Ah-battery.png


Higher voltage and higher Ah increases this, but you have a low of almost 1100A now with a single 3.2V cell.
 
This publication has a graph of a shorted 160Ah 3.2V LiFePO4 cell:

The-plot-of-current-and-temperature-during-short-circuit-of-LiFePO4-160Ah-battery.png


Higher voltage and higher Ah increases this, but you have a low of almost 1100A now with a single 3.2V cell.

So that’s approx 1000A

So would 4 cells have 4x the current?

My context is a 200Ah 4 cell 12V battery with an 250A MRBF terminal fuse
 
@Will Prowse - how about a video testing lithium max current and fuses, maybe some of the shittier breakers too

What happens if a Lifepo4 battery is shorted out? What is the max current? Is it 20,000 amps?

Do the various fuse types protect against a direct short. What does it look like if they don’t?

It would be important learning for folks, educational, interesting to see and has the potential to be quite entertaining ?

Could be a whole series, similar to the “will it blend” old skool you tube
This would be interesting-especially testing a couple of the more popular ones sold on Amazon!
 
This publication has a graph of a shorted 160Ah 3.2V LiFePO4 cell:

The-plot-of-current-and-temperature-during-short-circuit-of-LiFePO4-160Ah-battery.png


Higher voltage and higher Ah increases this, but you have a low of almost 1100A now with a single 3.2V cell.

I think I saw that before, and it seems way low to me. Can only draw 6C with zero volt dead short?
Common automotive starter battery would blow that away. They source 700 to 800A at 8.5V (?) for a 12V battery.
I've seen reported 4000A short circuit current from 100 Ah AGM.

This 160 Ah LiFePO4 single cell short-circuit current result doesn't pass the smell test. Maybe too much resistance in series?
I mean, it is possible the chemistry does this, but if so I doubt my 12V LiFePO4 jumpstarter the size of a lady's clutch could start a car.
 
Last edited:
I think I saw that before, and it seems way low to me. Can only draw 6C with zero volt dead short?
Common automotive starter battery would blow that away. They source 700 to 800A at 8.5V (?) for a 12V battery.
I've seen reported 4000A from 100 Ah AGM.

This 160 Ah LiFePO4 single cell short-circuit current result doesn't pass the smell test. Maybe too much resistance in series?
I mean, it is possible the chemistry does this, but if so I doubt my 12V LiFePO4 jumpstarter the size of a lady's clutch could start a car.

Yeah, same here - I'm just considering that to be the minimum, a lower bound so to speak. I wish I had time to do a short circuit test on one of my lab packs...
 
personally my current primary fuse plan for 12v and 24v LiFePO4 batteries is one MRBF mounted on each battery positive, in addition to one Class-T fuse upstream of all paralleled batteries, and sure to physically protect the inbetween wiring.
Do you use the same amp fuse for both MRBF and Class T fuse when you do this? I was thinking I could add a higher amp Class T fuse for short circuits along with an MRBF fuse? It would just be a way to save money on blown Class T fuses. Or have I missed something
 
Its been challenging sourcing 300-400A Class-T fuses for at least the last year. I haven't checked in the last month, but I don't think the shortage has eased much yet. In our shop, we've decided to use MRBF fuses on each battery for 12v and 24v systems coupled with main "system" fuses using type CNN and then MEGA fuses for each load or charger. We mostly use Victron components so this is relatively easy. Retrofitting large Class-A motorhomes is sometimes easier because they often come with appropriately sized Class-T fuses that we can use for the inverter/chargers.

We've been trying to move customers to 24v systems partly due to the cost savings and easier installation of smaller wiring, but also to give some extra headroom in wiring, fusing, etc. It's easier and safer to push around half the current, even if it means having to use DC-DC converters for 12v loads and a separate 12v battery with a DC-DC charger (LFP or AGM) for loads like hydraulic pumps and starting large generators. I'm looking at you @Lt.Dan :)

For 48v systems I feel like it starts to make sense, cost-wise, to use high AIC DC circuit breakers, especially since Class-T fuses have been hard to source. And a good DC breaker provides a manual disconnect. We're just now planning to dip our toes into the larger, off-grid stationary system space, so I haven't fully decided on the wisdom of this. I've considered the NOARK line of DC circuit breakers because they are relatively easy for me to source them here in the Midwest.

I don't mean to hijack the thread, but since we're talking about safety and high AIC current protection, I thought I'd put this out there.

Any critiques of these approaches? Thanks!
 
To assist consideration, here is a table of the various fuse types and their Ampere Interrupt Capacity at various voltages.
The data is sourced from Blue Sea Systems, specifically the 250A type, or the highest possible rated alternative. Links in the name type.

Type​
MSRP USD​
AIC per USD​
AIC @ 14V DC​
AIC @ 32V DC​
AIC @ 48V DC​
AIC @ 125V DC​
3​
333​
1,000 A​
MAXI
7​
142​
1,000 A​
8​
250​
5,000 A​
2,000 A​
12​
166​
2,000 A​
MRBF
19​
263​
10,000 A​
5,000 A​
2,000 A​
ANL
30​
200​
6,000 A​
45​
444​
20,000 A​

"AIC per USD" is calculated using MSRP and the 32V DC AIC Rating or the Next Highest Voltage AIC Rating. For Class-T, the 125V DC AIC Rating was used. Its units are Amperes Interruptable Per USD.

The AIC per USD is for comparing AIC value of different fuse types. According to the respective MSRP listed, the Class-T fuse is more AIC amps per dollar than all the other fuse types offered on that site. This is using MSRP listed on Blue Sea Systems, which might not reflect real prices available. All MSRP prices rounded up to the next one.

Hope this helps somewhat. I also needed to see this table ?
I'm late on this thread, but you should add the AMH fuse at 1400 AIC per USD.
The new king in the place when related to $/Breaking Capacity.
 
I'm late on this thread, but you should add the AMH fuse at 1400 AIC per USD.
The new king in the place when related to $/Breaking Capacity.
Will try to get to that today, thanks for mentioning it.
 
What's interesting about this subject is that you see very little about in builds on internet, youtube, etc. I bet you'd have a hard time finding a build/diagram that shows the use of Class T fuse or even MRBF for that matter. Only thing I see is about sizing fuse/breaker and if they do mention fuse it is ANL or MEGA. I wonder why
Not so fast there ..partner…every fuse I have is a classT ( 6 of 8 are shown here)… Or a class T tied in with a Buss mrcb so I have a cut off switch…. jus sayin.
 

Attachments

  • IMG_1042.jpeg
    IMG_1042.jpeg
    183.3 KB · Views: 61
To calculate AIC rating/need, divide the max cell voltage by the internal resistance in ohms to get amperes.

@Hedges mentioned 20,000 Amperes to be able to interrupt, but how to get to this number? 0.17 milliOhms was mentioned, and 3.65 Volts is the max LiFePO4 cell voltage. dividing 3.65 V by 0.00017 Ohm equals ~21,470 Amperes or about 20,000 Amperes.

if a given LiFePO4 cell had internal resistance of 1 milliOhm then the AIC needed would be 3.65 V / 0.001 Ohm equals 3650 Ampere or about 4000A.


this was my reference for how to know to divide voltage by ohms to get amperes
View attachment 113439


hope this helps!

one tip, not all internal resistance meters can accurately measure internal resistance in Ohms on large capacity cells like 300Ah cells and alternate methods can be used to get more accurate data for those kind of cells.
You are leaving the BMS out of the resistance total. My Overkill BMS has 3x 8awg 12" wires in and 3x 8awg 12" wires out, that's close to 24" of 3awg (0.427 milliohms). The PCB and solder also has resistance, and so will the FETs even when shorted. In fact the BMS has a 3 stage shutdown. One is slow software based for it's max current rating. The 2 hardware limits are much faster and have higher current limits to prevent false tripping from noise. If it failed to shut down you need the fuse, the BMS FETs are shorted.
 
Last edited:
In my Travel Trailer I am not using a high power inverter, just a 300w model. I only needed 4awg per Overkill
Solar (0.427 milliohms) minimum guidelines for RED wire (0.45 milliohms) and my fuse choice of 150A ANL (0.3 milliohms). I put 1 fuse in each of 2 battery boxes with the cells. The 4 trunk lines are 4awg each, about 4ft (2 milli ohms each battery), 2 to Shunt, 2 to another 150A ANL. Also routed thru separate holes in wall to pass thru storage - power panel. Shorts are unlikely and the boxes are bolted down to better tolerate road accidents.

(0.427 milliohms) + (0.45 milliohms) + (0.3 milliohms) + (2 milli ohms battery wire) = 2.777 milliohms. at 13v = 4693 AIC.
But this leaves out the BMS circuit board, solder, FET, also interconnect resistance of battery bus bars and bolt down wire lugs. Also the final 150A ANL (0.3 milliohms) on the power panel, and the Shunt (0.1 milliohms).

Still I am nervous about having ANL vs. Class T. I'm keeping these batteries and avoiding the liability of passing them on when I sell this Travel Trailer. Some fool may upgrade the wire AWG and not the fuses.
 