24V no problem, inverter and battery can be 24V.Thanks for your help, but I’m stuck with a 24 V inverter that I just bought. I got a Victron 24 V inverter. So I’ll have to try to do what I posted with three strings and three charge controllers.
for me I have to keep it very simple, as I’m not as knowledgeable as most. Again thanks for all your help. ??
Charge controller can be set for 24V (or maybe automatically detects 24V battery) as its output voltage.
What I'm saying is, for a 24V system, you should connect your PV panels as 48V or 72V. The charge controller will act like a transformer and drop that to 24V at higher amps and charge the battery.
The battery may range between 22V and 32V depending on depth of discharge/state of charge. And rate (current) of charge or discharge.
A "24V" PV panel may range between 27V and 45V depending on temperature and current draw. It requires a charge controller to regulate battery voltage, and MPPT charge controllers are particularly good and extracting maximum power over a wide temperature range. They also let you run higher voltages (more panels in series, fewer in parallel) so you can use smaller wires and sometimes no fuses. But a "24V" panel will not work very well to charge a 24 battery, at least not with an MPPT charge controller.
The drawing I gave you with four 12V panels and two 24V panels will work for you. It just leaves one 24V panel unused.
You can add to it. If you buy four more panels, 320W 24V, you can add those. Two in series for 640W 48V, add in parallel with the existing 48V strings. Do it again for another 640W 48V. Use a 15A fuse for every string, now for fuses in total.
4 x 150 = 600W
2 x 300 = 600W
2 x 320 = 640W
2 x 320 = 640W
(All are 48V nominal)
All of these strings connected in parallel and fed into the charge controller is:
600 + 600 + 640 + 640 = 2480W at 48V
They won't actually produce the full 2480W except on a cold bright day. More like 2000W most of the time.
The Renogy charge controller can't make use of all 2000W, so as the sun comes up, power will increase to 1500W and stay flat until later in the day.
But I have a way to avoid wasting any power.
Orient two of the strings at 10:00 AM sun.
Orient two of the strings at 4:00 PM sun.
Half the panels are now at a 90 degree orientation to the other half. They never make full power at the same time, but some make more early and some make more later.
This setup will have about 1600W of peak production on a cold sunny day, more like 1400W peak in normal weather. That is just under the Renogy's max output, so a single charge controller will handle all of them effectively.