That, and zombie Isaac Newton or your favorite 19th century electrical scientist/engineer.Physics police means fire department and insurance company, right?
That, and zombie Isaac Newton or your favorite 19th century electrical scientist/engineer.Physics police means fire department and insurance company, right?
Missouri -20Need to know the lowest temps possible, and the temperature voc coefficientSolar Panel Maximum Voltage Calculator - Footprint Hero
Calculate the maximum open circuit voltage of your solar array. Find your max solar panel voltage to correctly size your solar charge controller.footprinthero.com
I have close to 20kw of these panels for future setup when house is built. I’m just trying to use this 6kw hybrid inverter with 145v max because it’s been collecting dust for about a year now. The 6kw output works for me for a temporary setup. Just trying to get the solar input to the max I can safely.This is unhelpful, but when I went back and saw 535W panels were being used, I thought, "This is really a Great power / Great responsibility situation; if you want to use things that big you should also do big investment in planning & researching up front." Vs the safety of numbers of using standard normal residential sizes (and by extension voltage/currents) like 400W +/- 50W.
#10 was also the wrong choice if starting with the cell size with 13A I_mpp and a non-trivial probability of going to parallel strings.
The difference in voltage drop between 94V and 142V is insignificant. The main determining factor in voltage drop is amperage. If you add another PV circuit (2s3p/3 circuits) you will have the same average per circuit as 3s2p. It might be cheaper to buy a higher voltage mppt then the wire depending on the run length assuming you sell the other one. Unless you have an all in one inverter/mppt (unless it's a modular one ex: Outback Solar).I can’t do 3s2p. The distance is too far and the voltage will be too low for my 10 gauge wire. I need the voltage to be on the higher side to keep amps down to get away from running long distance. That’s why I went with 2s3p. If I was to running 3s2p then I will have to run 8-6 gauge wire to be under the 3 percent voltage drop.
To summarize my contributions to the threadI have close to 20kw of these panels for future setup when house is built. I’m just trying to use this 6kw hybrid inverter with 145v max because it’s been collecting dust for about a year now. The 6kw output works for me for a temporary setup. Just trying to get the solar input to the max I can safely.
Hello everyone. Need to reduce solar voltage on my temporary system. Running 2 sets of (3) 535 watt panels. Controller voltage is 145 max. I hitting that mark. On warmer days I get around 139-140v. This week was colder so I hit the 145-150v mark. I need to drop voltage by 5-10v before going into controller. Any ideas? For now I unplugged 1 panel off each array. Running 3 sets of 2 panels is out of question because of the distance between controller and arrays. View attachment 179235View attachment 179236
He never said how had the panels wired up from say a combined box or mc4 splice to the SCC.The difference in voltage drop between 94V and 142V is insignificant. The main determining factor in voltage drop is amperage. If you add another PV circuit (2s3p/3 circuits) you will have the same average per circuit as 3s2p. It might be cheaper to buy a higher voltage mppt then the wire depending on the run length assuming you sell the other one. Unless you have an all in one inverter/mppt (unless it's a modular one ex: Outback Solar).
I’m not running the entire system on only (1) set of 10 gauge wire bro. I’m running 2 sets of wires (3 panels) 160ft and second set of wire 100ft distance. And that’s total lengths including positive and negative runs. More than sufficient for 2s3p.To summarize my contributions to the thread
2s1p to comply with NEC Isc limits on #10
2s2p if you don't care about that and just care about not smoking the MPPT
I’m not running the entire system on only (1) set of 10 gauge wire bro. I’m running 2 sets of wires (3 panels) 160ft and second set of wire 100ft distance. And that’s total lengths including positive and negative runs. More than sufficient
2s2p is 4 panels and 3s2p is 6.2s2p or 3s2p.
Orient strings differently so the don't all make max current at the same time.
10 awg 90 degree C wire actually has ampacity 40A; it is only the code police who say 30A.
Code says Isc x 1.56, but that's related to nuisance tripping of thermal breakers.
Magnetic-hydraulic breakers don't need the second 1.25x for nuisance trip. That leaves just 1.25x for cloud edge effects (not 1.56x).
Anything beyond that is code writers, not physics or engineering.
Or buy a higher voltage charge controller, as suggested, and let that charge the battery feeding your inverter.
2 sets of wire is two strings not three.So
How do the two strings of 10awg connect to the SCC?
2 Y Branch Connectors before controller. Then single wires through pv breaker then to controller. From Y connectors to controller it’s about 6 feet of total wire. That’s 26 amps running at 126v at normal operating conditions through 6 feet of wire.So
How do the two strings of 10awg connect to the SCC?
You need bigger wire... Go 6ga or go home.I can’t do 3s2p. The distance is too far and the voltage will be too low for my 10 gauge wire. I need the voltage to be on the higher side to keep amps down to get away from running long distance. That’s why I went with 2s3p. If I was to running 3s2p then I will have to run 8-6 gauge wire to be under the 3 percent voltage drop.
I think it’s a misconception that a ssc will start smoking if supplied over-voltage. My controller personally will not supply any charge with overvoltage. It just cuts pv input off when over 145v. Can’t say this about all scc are this way.To summarize my contributions to the thread
2s1p to comply with NEC Isc limits on #10
2s2p if you don't care about that and just care about not smoking the MPPT
Sarcasm? Lol Explain why I need thicker wire with running 2s3p setup I have?You need bigger wire... Go 6ga or go home.