Hello everyone, we have the following challenging situation with our offgrid cabin setup, highly appreciative of any tips / help / questions from you!
We are expanding our electrical installations in a new building extension. The electrical panel had 5x10A 1x16A, now we are trying to add 3x10A and 6x16A for the new.
((Needless to say, our inverter is much to small for all of this and at some point must be upgraded to something bigger))
The issues started when our electrician (not familiar with offgrid at all) needs to make formal measurements of voltages and of short circuit current (amperage).
Firstly, he measured 80V in the N wire and 150 in the L (delta being 230V), which threw a fault in the "Fluke" meter he was using.
Then, after installing a proper grounding rod and connecting the ground to N in the electrical panel, the N was 0V and the L 230V, and the Fluke-meter was happy to start measuring short-circuit currents.
==> However, here the real problems started. Per regulation, our six 16A fuses require at least 100A short circuit current, and he was not able to get any Fluke-readings over 80A. (With effort, the three 10A fuses needing >62,5A passed their tests).
Any tips, thoughts, tricks, ideas?
* should we bond the neutral and ground in / at the inverter, or in the electrical panel (as-is)?
* Or must we change the inverter to a new one?
* Have newer (larger) inverters solved the issue of ground-neutral-bonding to secure zero volts in the neutral?
* Will bigger inverters create higher current results in such tests?
* Is it the age of the inverter which was creating the voltage skew from N0V/L230V to N80V/L150V? If yes, why do old inverters slide into this type of fault?
Here's the setup: MPP Solar's PIP-3024GK (3kW/24V installed 2018), 8x285Wp solar (2018), 3 LFP batteries (~100+135+280Ah, from 2020 and 2023), EU system i.e. 230V AC at 50Hz.
We are expanding our electrical installations in a new building extension. The electrical panel had 5x10A 1x16A, now we are trying to add 3x10A and 6x16A for the new.
((Needless to say, our inverter is much to small for all of this and at some point must be upgraded to something bigger))
The issues started when our electrician (not familiar with offgrid at all) needs to make formal measurements of voltages and of short circuit current (amperage).
Firstly, he measured 80V in the N wire and 150 in the L (delta being 230V), which threw a fault in the "Fluke" meter he was using.
Then, after installing a proper grounding rod and connecting the ground to N in the electrical panel, the N was 0V and the L 230V, and the Fluke-meter was happy to start measuring short-circuit currents.
==> However, here the real problems started. Per regulation, our six 16A fuses require at least 100A short circuit current, and he was not able to get any Fluke-readings over 80A. (With effort, the three 10A fuses needing >62,5A passed their tests).
Any tips, thoughts, tricks, ideas?
* should we bond the neutral and ground in / at the inverter, or in the electrical panel (as-is)?
* Or must we change the inverter to a new one?
* Have newer (larger) inverters solved the issue of ground-neutral-bonding to secure zero volts in the neutral?
* Will bigger inverters create higher current results in such tests?
* Is it the age of the inverter which was creating the voltage skew from N0V/L230V to N80V/L150V? If yes, why do old inverters slide into this type of fault?
Here's the setup: MPP Solar's PIP-3024GK (3kW/24V installed 2018), 8x285Wp solar (2018), 3 LFP batteries (~100+135+280Ah, from 2020 and 2023), EU system i.e. 230V AC at 50Hz.