$1200 of circuit breakers???
Do you mind sharing your cost breakdown?
Sure. That figure was from memory from about 8 or so months ago, when I was considering the Watts/Amensolar inverter, which also does not have breakers in its wiring box.
You will need:
2 - DC 250A 1-pole battery breakers (or a dual pole one) at about $300 (for Midnites)
3 or 4 (one dual pole DC breaker per MPPT input at your max V) at about $200 (again for Midnites, ~$50 ea)
1 - 125A (+/-) dual pole AC breaker for grid in at about $80 ( varies by brand)
1 - 100A (+/-) dual pole AC breaker for grid out to load at about $80 ( varies by brand)
1 - 60A (+/-) dual pole AC breaker for generator in at about $50 ( varies by brand)
And depending upon what other in/outputs your inverter has, various other single and dual pole breakers
so somewhere between $20 to $50 each.
So I have $600-700 worth of breakers, and to that you'd need to add the cost of the electrical boxes they go in, fittings and conduit, wire, etc. Maybe doubling the breaker costs was a bit high, but I bet it comes close to $1k total, plus the hassle of all that extra wiring.
Now your specific installation may not need all of these. You may already have them from your old system. Or some of the output load breakers may be handled via a main breaker in the panels (though that incurs some extra cost too). Or you may be willing/able to use cheap non-UL Chinese parts which will save quite a bit.
Anyway that is how I came up with my numbers. Let me know if you think this is way off.