What is the model number of the inverter?
What is the model number of the battery?
Your title implies new install. How new? Has it ever run the pump on battery power?
ThanksWhen you say the battery could be overcharged, is that because of too high of charging current or too high of float voltage?
You might try the AGM setting, it has a lower float voltage.
In a backup plan as you have, it would seem that float voltage is the main issue. When you power up, it will run through the boost then sit there in float waiting for an outage. I would limit the testing of the system because each time you test it, it will run the boost again.
Hello! The battery setting was at 3 and still in boosting mode when the issue happened (red flashing of battery led). ii will try the setting at 2 (agm) on the inverter as you suggested. The charging boost os slighly over the 55.5, but floating is perfect.When you say the battery could be overcharged, is that because of too high of charging current or too high of float voltage?
You might try the AGM setting, it has a lower float voltage.
In a backup plan as you have, it would seem that float voltage is the main issue. When you power up, it will run through the boost then sit there in float waiting for an outage. I would limit the testing of the system because each time you test it, it will run the boost again.
hello! The inverter is doing well with the surge...it is a 6000 watt with 300% surge capacity. The issue is with the charging mode setup of the inverter.Pumps with standard induction motors have high surge currents and are sometimes difficult to start with an inverter. There are 3 solutions.
1) Variable speed pump with built in VFD which ramps up to speed.
2) Soft Starter module if the pump motor is compatible with such a device and the wiring is accessible, not down in the well.
3) Use an oversized, Low Frequency inverter with a BIG transformer.
Hello! i faced another issue whith the new system...the inverter was set at 9...cv 50.25, no float...the battery was getting slowly charged no issue...however, this time, it was the inverter that went in overload. The only item on the system was the well pump...is it possible that it was to much for the inverter to charge while supporting the pump?When you say the battery could be overcharged, is that because of too high of charging current or too high of float voltage?
You might try the AGM setting, it has a lower float voltage.
In a backup plan as you have, it would seem that float voltage is the main issue. When you power up, it will run through the boost then sit there in float waiting for an outage. I would limit the testing of the system because each time you test it, it will run the boost again.