ericfx1984
- Oct 10, 2021
- 741
I have an Aims power 3,000 W inverter...
That is hooked up hardwired to my RV (30 amp)
I'm also building a completely off-grade house and I just finished the 120 side of the electrical
I figured the easiest way to test the 120 circuits was to install a double breaker (normally used for 240v) to backfeed the 120 hots into that breaker effectively bonding both sides of the breaker box
When I first plugged it up even with all the breakers off it immediately tripped the GCFI on the inverter
I also tried this test using my generator which also had the same problem
So I figured it had to be something on either the neutral or ground side of things... I figured this was the case since all of the hots were switched to off
I quickly discovered that it was an issue with the breaker box having a bonded neutral
The only way that I could actually get power to go through the breakers was to disconnect the ground feed going from the generator to the breaker box
Since this is not going to be hooked up to grid ever, what is the best way to do this? I'm guessing I would want to install a proper ground rod for the house and tie the inverter to that ground rod as well as the house to the ground rod? I guess this is the part I'm having a little trouble understanding?
With the RV I simply let the inverter handle the ground side of things and everything just sort of works and maybe that's the answer
Anyway I'm not quite sure I would love to have someone's opinion