OUTBACK MPPT 80 FLEXPOWER

The Schneider shows the battery bank is a 48 volt system . And fully charged at 53.3 volts
 

Attachments

  • IMG_4682.png
    IMG_4682.png
    349.9 KB · Views: 6
  • IMG_4681.png
    IMG_4681.png
    302.1 KB · Views: 6
The Schneider inverter and Outback charge controller have different wires and different fuses, right?

This is like saying, my neighbor's house has power so mine must too. You can't relate those two facts without testing. There are failure points between the two.

Can you please just measure the voltage at the charge controller? Like has been requested.
Check your fuses or breakers.

A failed fan isn't going to cause the low voltage readings.
 
Also if he is pushing the 60 plus volts from the Outback it should shut the batteries down. In theory.
 

Attachments

  • IMG_4683.png
    IMG_4683.png
    589.6 KB · Views: 1
Also if he is pushing the 60 plus volts from the Outback it should shut the batteries down. In theory.
That was probably open circuit voltage output from the charge controller, before it reacted to the open circuit and dropped battery voltage down to near 0
 
According to the display on your Outback mppt 80, it sees 1.9V coming from battery.
If correct, that could be why it doesn't work.

Please put a DMM on the battery terminals of the Outback and tell us what voltage is there.
If different from voltage of battery itself, check with DMM to find a bad connection.
 