Question about breaker use for 3+ parallel strings:
I understand the following:
1. When combining two series strings, no OCPD is needed, as in the case of a short circuit in the first string, the second string can only push the max of the Isc amp rating of a string into the first, which is less than the max series fuse rating.
2. When dealing with more than two parallel strings (let's say three for simplicity), if there is a short in the first string, then the other two can each push a max of ISc (or just max current at max power) amps into the shorted one, and 2xIsc (or even just 2x current at max power) is greater than the maximum series fuse rating, this requiring an OCPD device on each string.
3. What I don't understand is, why vendors such as MIdnite provide combiners that accept breakers, such as the MNEPVxx series, which are polarized (only break in a single direction, and appear to show the + side toward the PV) hence in the case of a short, the high current would come from the *wrong* direction, which causes the breaker to not put out the arc, or worse, a fire.
I know there are fuse solutions that work in both directions (as opposed to breakers), but why the option for polarized breakers in this case in systems such as the MNPV3 or 6 combiners, and probably other combiners? I also know that MIdnite is advertising some non-polarized breakers that are not yet generally available.
Reference for this saying not to use polarized breakers in this situation:
I suspect this has already been discussed, and if so, I apologize, and ask to be pointed to said posts. Thanks.
I understand the following:
1. When combining two series strings, no OCPD is needed, as in the case of a short circuit in the first string, the second string can only push the max of the Isc amp rating of a string into the first, which is less than the max series fuse rating.
2. When dealing with more than two parallel strings (let's say three for simplicity), if there is a short in the first string, then the other two can each push a max of ISc (or just max current at max power) amps into the shorted one, and 2xIsc (or even just 2x current at max power) is greater than the maximum series fuse rating, this requiring an OCPD device on each string.
3. What I don't understand is, why vendors such as MIdnite provide combiners that accept breakers, such as the MNEPVxx series, which are polarized (only break in a single direction, and appear to show the + side toward the PV) hence in the case of a short, the high current would come from the *wrong* direction, which causes the breaker to not put out the arc, or worse, a fire.
I know there are fuse solutions that work in both directions (as opposed to breakers), but why the option for polarized breakers in this case in systems such as the MNPV3 or 6 combiners, and probably other combiners? I also know that MIdnite is advertising some non-polarized breakers that are not yet generally available.
Reference for this saying not to use polarized breakers in this situation:
I suspect this has already been discussed, and if so, I apologize, and ask to be pointed to said posts. Thanks.