@Carlos_Sol-Ark are you listening?
Yeah Haha I'm here, I just get off at 6 pm Central time. Also monitoring the forums is more like a third priority to my other duties so I may be a bit slow to respond sometimes, but
I will get back to you. I certainly hear the point you are making.
There is no "check if AC source on grid input is grid or gen"
The Sol-Ark checks every AC connection it makes on the GRID terminals to determine GEN or GRID status.
The grid monitoring and reaction are magnitudes faster than this. I can't give you the exact response time, but I was told anyone is welcome to use an oscilloscope on their units. Once the Sol-Ark disconnects it will initiate a default 300S delay before reconnecting to any new AC source, you can lower it if you like but I wouldn't recommend anything lower than 60S. This should answer the question of a possible mis-phase connection.
Or how about this... how about Sol-Ark changes their hardware to support gen shave. Now we could set gen shave to 10kW to stay under the gen's rating, 95% of the time the gen runs it's pushing (10kW - average 4kW load) ~6kW to the batteries. Thsi setup works absolutely perfectly with Schneider, Outback, Magnum, Victron, Midnite Rosie inverters and probably many others.
I have recently been assigned to a group of app engineers who can do testing specifically for our residential systems so I think I can get some testing done to solve the battery charging problem you brought up here. In the past, the options available would be either the customer would have to adjust or monitor their loads during generator to battery charging, or they would charge the batteries slowly and use Time of Use to set an AC charging cap and have the generator stop charging the battery at a certain point. This would allow the generator to run for a shorter time, but keep the batteries going until solar power returns. Most people do the latter if they are strictly off the grid.
If they are on the grid most of the time and they want to use the batteries while grid-tied to offset loads, but they also want to have the generator kick on during a long-term outage to charge the batteries back up when they get low, but their generator isn't big enough to cover loads and fast battery charging, and they are not able to manage loads or are not on sight, they can still use Time of Use to make sure the generator doesn't stay on too long. However, there will be compromise as to how high the generator charging cap while off-grid would be and how low the batteries can get when off-setting the loads when grid-tied.
Note: I am not the head honcho, but I am here to listen to use-case issues exactly like this. This is gold to me, and I am on forums like this to find out what we can do to make the Sol-Ark easy to use in as many applications as possible. Well that and answer questions
Summary so far:
- Generator Terminals Can not do 3-phase connections, but the Grid terminals can due to hardware differences between Gen and Grid terminals on the Sol-Ark.
- Sol-Ark will be able to break the connection from the 3-phase transfer switch from the generator to the grid fast enough to prevent a connection to a mismatched phase. ---- STILL USE BREAK BEFORE MAKE ATS.
Use case problems I will try to find solutions/answers for:
- Sol-Ark Generator relay staying closed after grid connection status is re-made.
- GEN Peak Shaving equivalent????? I need to confirm why we stopped supporting it in the first place. It certainly wasn't due to a hardware change.