I'm testing new 6000xp inverter. Tied to 4 LifePO4 12v 280ah. Batteries connected in serial for 48v (no communications). As has been discussed in other threads, I set the battery type on the inverter to lead acid (Is that why the percentage read 82% full in this snapshot when the batteries reported 100%?)
Question: Inverter says I'm pulling about 20 watts continually. If I look at the BMS on each, they read about 12-19 Watts each. Here is one of the batteries show 15 watts. Also batteries now show 82% which means I've used 18% for 0.9kw (in the battery discharge above). Doesn't this mean I'm only looking at getting .9kw/.18%=5kw out of the batteries when I should be getting 280ah*12*4=13440?
Thanks
Question: Inverter says I'm pulling about 20 watts continually. If I look at the BMS on each, they read about 12-19 Watts each. Here is one of the batteries show 15 watts. Also batteries now show 82% which means I've used 18% for 0.9kw (in the battery discharge above). Doesn't this mean I'm only looking at getting .9kw/.18%=5kw out of the batteries when I should be getting 280ah*12*4=13440?
Thanks