Does the body of the breaker get very hot at full load?
BTW, What is the spec of the panel?
You have 80A breaker and you are pulling less than half of the breaker spec, may be defective breaker, I see that has a link that joint the breaker handles together, I wonder if you can remove the clear plastic linker that join the breaker for the positive and the negative breaker together and see which one will trip.
If you have clamp-on DC Amp meter with peak hold reading then you use it to monitor the current to see what you get.
BTW, What is the spec of the panel?
You have 80A breaker and you are pulling less than half of the breaker spec, may be defective breaker, I see that has a link that joint the breaker handles together, I wonder if you can remove the clear plastic linker that join the breaker for the positive and the negative breaker together and see which one will trip.
If you have clamp-on DC Amp meter with peak hold reading then you use it to monitor the current to see what you get.