Dear folks,
Hope my post finds you well.
Hope someone share me his experience with the buggy Revo II inverter.
I have around 50 inverters installed in diff sites.
Inverter settings:
The issue is as follows:
Batteries are empty, load is around 5 amps, the inverter is charging batteries with few amps like 7 amps or less where they are EMPTY and covering the load of home around 5 Amps. Load of PV is around 30% of its Max true power.
If u make home load, the PV power will significantly increase to cover load (up to 5000 watt from PV)
The charging from PV is set to 90 Amps. but never went above 15 amps because Mr. Revo doesnt want to make load on him self to charge batteries from PV.
If utility came up, the inverter will start charging batteries according to the charge setting on AC (if its set to 60 Amps, it will charge @60 amps to the batteries)
So why this inverter not want to use the PV true power to charge batteries?
Talking to sorotech but never came up with single solution.
Hope to hear from you!
Thanks and regards.
PS. this issue is only in the OFF Grid Mode.
Besides, never ask me in Parallel how one unit is daring batteries, and other one is charging! (Same PV power on both inverters)"OFF grid Mode Only".....
Hope my post finds you well.
Hope someone share me his experience with the buggy Revo II inverter.
I have around 50 inverters installed in diff sites.
Inverter settings:
- Off Grid Mode (Even no utility)
- Work mode: AC - PV
- Charge settings on PV is 90 Amps , while on AC is set to 60 Amps
- 4 or 8 Batteries Luminus or Tuff Bull 220 Amps Lead Acid.
- 9 Panels in series 535 Longi Hi-Mo5 Bi-facial giving real power around 5000 watt (Peak time)
The issue is as follows:
Batteries are empty, load is around 5 amps, the inverter is charging batteries with few amps like 7 amps or less where they are EMPTY and covering the load of home around 5 Amps. Load of PV is around 30% of its Max true power.
If u make home load, the PV power will significantly increase to cover load (up to 5000 watt from PV)
The charging from PV is set to 90 Amps. but never went above 15 amps because Mr. Revo doesnt want to make load on him self to charge batteries from PV.
If utility came up, the inverter will start charging batteries according to the charge setting on AC (if its set to 60 Amps, it will charge @60 amps to the batteries)
So why this inverter not want to use the PV true power to charge batteries?
Talking to sorotech but never came up with single solution.
Hope to hear from you!
Thanks and regards.
PS. this issue is only in the OFF Grid Mode.
Besides, never ask me in Parallel how one unit is daring batteries, and other one is charging! (Same PV power on both inverters)"OFF grid Mode Only".....