I have a 6K eg4 running seemingly well for about 10 days. I recently lost my Microwave and had to upgrade to a Samsung 1600w input. AME811CST.
Now when I started the microwave today I got an error 52. Batteries 2x5kw eg4 were full. And 2300w of solar was coming down. 52 is Bus Voltage too Low
I power cycled and tried again and it worked. Could this be that the microwave for some reason even though it's the only thing on the leg. Takes it from 130-1.6KW. BUT the kVA goes from 160-2.6kw at the start?
Why is the kVA so wildly different to he watts. And it puts the load at 100% almost on that leg.
Also is the 6KW being phased out by signature solar? Seen it disappeared from their site.
Now when I started the microwave today I got an error 52. Batteries 2x5kw eg4 were full. And 2300w of solar was coming down. 52 is Bus Voltage too Low
I power cycled and tried again and it worked. Could this be that the microwave for some reason even though it's the only thing on the leg. Takes it from 130-1.6KW. BUT the kVA goes from 160-2.6kw at the start?
Why is the kVA so wildly different to he watts. And it puts the load at 100% almost on that leg.
Also is the 6KW being phased out by signature solar? Seen it disappeared from their site.