Carlos_Sol-Ark
- Jul 20, 2022
- 47
Whenever you dont see the SOC or Voltage options in the Time of Use menu it is usually an indicator that you are in Closed Loop Communications (Lithium Batt Mode on the Inverter). We do not have closed-loop communications with the Soho telecom batteries so make sure you remove the communication cable (important) and select either Use battery % charged or use batt V charged on the Sol-Ark. That should help a lot with strange issues.Oh. I see. Except I have batteries and I think I configured TOU to draw from the batteries. Maybe I've done it wrong. According to Solar-Assistant, there's only been a few hundred mA going into the batteries.
The Sell check boxes tell the inverter that it is allowed to sell the battery power to the utility. If 4000W is programmed with the sell check box in a Time Slot, the inverter will constantly push 4000W out from your batteries. In this case when you have 1500W of loads, then only 2500W gets sold to the utility. If you have 6000W of loads nothing gets sold, but the inverter will still cover 4000W of the load while the grid contributes 2000W. You should never have both the Charge and the Sell Check boxes selected in the same time slot.Also, under TOU, if you don't have Sell selected for the time you want battery, I don't think it uses batteries.
I have all mine set to sell. It will use battery until it gets to the limit. If it goes below the limit, say from multiple cloudy days and trickle loss, it will use solar for battery only until it gets the batteries back up to the minimum, then solar for load first, then batteries after load is satisfied.
@hpeyerl DM me your inverter SN and I will take a look on PowerView for you.