Im looking to build a roof mounted breaker box for my 2 solar arrays. It will also house my 2 Midnight solar SPD's.

I was planning on using the below Phoenix distribution blocks to properly tie in the SPD's before the breakers.
-S1400x1400-FJPG


They are rated for 690V and 24A.

I plan on having 8 panels at 43VOC and 13.73A. Totaling 344VOC.

I was considering using these terminal blocks for the ground too, but concerned that if i do receive a lightning strike or surge, the block wouldnt be able to handle it.

Should I stick with a typical ground bar?

Do you see any issues using these terminal blocks?
 

Attachments

  • IMG_7713.JPG
    IMG_7713.JPG
    852.9 KB · Views: 1
Those should be fine, for ground consider din rail mounter ground terminal blocks, these bond to the metal of din rail for the ground connection. If not that I would use a standard ground bar.
 
It's a potential failure point. I would have absolutely nothing between the ground rods, and the main grounding bussbar. The main grounding conductor should be a single unspliced copper cable from one end to the other.
 