I have been working on my own off grid system the past few months and am new to solar. My system consists of 2 SunGoldPower TP6048 6KW Inverter/chargers in parallel (which have been a nightmare, but that is for a different post) and 48 used Solarworld SW245 Mono panels. The panels are connected 12s2p to each inverter to be at the max inverter input voltage of 450v and just under the power max at 5,880 watts (at full performance). Since this is still a work in project, I currently have the panels flat on the ground and I live in North Texas.
The thing I am questioning in the performance of the inverter and panels. When I tested the panels, they were all around the specified Voc at 36-37vdc. The current for each was measuring around 6 amps. When I measured one series string, it was around 430vdc and the current was still around the 6 amps. Once I connected it to my inverter however, the voltage remained the same but the current dropped down to around half the measured current when disconnected. Is this normal?
Because of this, my roughly 12kw of panels have produced 6kw at the peak (which may have been in October when I first set the system up.
I'm trying to figure out if my junk inverters have yet another problem since they won't accept the full amperage the panels put out, or if this should be expected until I get the panels mounted on rails at the proper angle.
Thanks!
The thing I am questioning in the performance of the inverter and panels. When I tested the panels, they were all around the specified Voc at 36-37vdc. The current for each was measuring around 6 amps. When I measured one series string, it was around 430vdc and the current was still around the 6 amps. Once I connected it to my inverter however, the voltage remained the same but the current dropped down to around half the measured current when disconnected. Is this normal?
Because of this, my roughly 12kw of panels have produced 6kw at the peak (which may have been in October when I first set the system up.
I'm trying to figure out if my junk inverters have yet another problem since they won't accept the full amperage the panels put out, or if this should be expected until I get the panels mounted on rails at the proper angle.